Configuration data
Index 80n0 DPM Channel Settings (for Ch.1, n = 0; Ch.2, n = 1; Ch.3, n = 2; Ch.4, n = 3; Ch.5*, n = 4; Ch.6*, n = 5)
80n0:0 | DPM Channel Settings | Max. Subindex | UINT8 | RO | 0x16 (22dec) |
80n0:11 | Supply Channel | Selection of the voltage reference: 0: No Supply | UINT32 | RW | UL1 / UL1L2 (1) |
80n0:12 | Current Transformer Ratio | The ratio of the current transformer used can be entered here. | REAL32 | RW | 1.000000 (1.000000e+000) |
80n0:13 | Current Transformer Delay | Here you can enter a possible time delay of the current transformers in milliseconds [ms]. | REAL32 | RW | 0.000000 (0.000000e+000) |
80n0:14 | Power Calculation Threshold | Noise reduction: Threshold values for the corresponding warn bits Here you can enter a minimum limit value in percent for the power calculation, below which all values are zeroed.[%] | REAL32 | RW | 0.000000 (0.000000e+000) |
80n0:15 | Inaccurate Threshold Current | Limit value for the warning bit: Inaccurate Current | REAL32 | RW | 0.006000 (6.000000e-003) |
80n0:16 | Measurement Range | The frequency range to be used can be selected here [Hz] Permitted values: 0: 45..65 Hz (default) | REAL32 | RW | 45..65 Hz (0) |
*) only EL3446 | |||||
Index 80n1 DPM Channel User Scale (for Ch.1, n = 0; Ch.2, n = 1; Ch.3, n = 2; Ch.4, n = 3; Ch.5*, n = 4; Ch.6*, n = 5)
80n1:0 | DPM Channel User Scale | Max. Subindex | UINT8 | RO | 0x13 (19dec) |
80n1:01 | User Calibration Enable | Set to true to enable user calibration data. | BOOLEAN | RW | 0x00 (0dec) |
80n1:11 | User Calibration Current Offset | Value in A | REAL32 | RW | 0.000000 (0.000000e+000) |
80n1:12 | User Calibration Current Gain | Factor (without unit) | REAL32 | RW | 1.000000 (1.000000e+000) |
80n1:13 | User Calibration Phase Offset | Value in milliseconds | REAL32 | RW | 0.000000 (0.000000e+000) |
Index 80n2 DPM Channel Guard Settings (for Ch.1, n = 0; Ch.2, n = 1; Ch.3, n= 2; Ch.4, n = 3; Ch.5*, n = 4; Ch.6*, n = 5)
80n2:0 | DPM Channel Guard Settings | Max. Subindex | UINT8 | RO | 0x14 (20dec) |
80n2:01 | Voltage Guard Min Error | Lower limit value for a voltage error message [V] | REAL32 | RW | 2.000000 (2.000000e+000) |
80n2:02 | Voltage Guard Min Warning | Lower limit value for a voltage warning message [V] | REAL32 | RW | 207.000000 (2.070000e+002) |
80n2:03 | Voltage Guard Max Warning | Upper limit value for a voltage warning message [V] | REAL32 | RW | 253.000000 (2.530000e+002) |
80n2:04 | Voltage Guard Max Error | Upper limit value for a voltage error message [V] | REAL32 | RW | 278.000000 (2.780000e+002) |
80n2:05 | Current Guard Min Error | Lower limit value for a current error message [A] | REAL32 | RW | -1.050000 (-1.050000e+000) |
80n2:06 | Current Guard Min Warning | Lower limit value for a current warning message [A] | REAL32 | RW | -1.000000 (-1.000000e+000) |
80n2:07 | Current Guard Max Warning | Upper limit value for a current warning message [A] | REAL32 | RW | 1.000000 (1.000000e+000) |
80n2:08 | Current Guard Max Error | Upper limit value for a current error message [A] | REAL32 | RW | 1.050000 (1.050000e+000) |
80n2:09 | Active Power Guard Min Error | Lower limit value for an active power error message [W] | REAL32 | RW | -241.500000 (-2.415000e+002) |
80n2:0A | Active Power Guard Min Warning | Lower limit value for an active power warning message [W] | REAL32 | RW | -230.000000 (-2.300000e+002) |
80n2:0B | Active Power Guard Max Warning | Upper limit value for an active power warning message [W] | REAL32 | RW | 230.000000 (2.300000e+002) |
80n2:0C | Active Power Guard Max Error | Upper limit value for an active power error message [W] | REAL32 | RW | 241.500000 (2.415000e+002) |
80n2:0D | Apparent Power Guard Min Error | Lower limit value for an apparent power error message [VA] | REAL32 | RW | 0.000000 (0.000000e+000) |
80n2:0E | Apparent Power Guard Min Warning | Lower limit value for an apparent power warning message [VA] | REAL32 | RW | 0.000000 (0.000000e+000) |
80n2:0F | Apparent Power Guard Max Warning | Upper limit value for an apparent power warning message [VA] | REAL32 | RW | 230.000000 (2.300000e+002) |
80n2:10 | Apparent Power Guard Max Error | Upper limit value for an apparent power error message [VA] | REAL32 | RW | 241.500000 (2.415000e+002) |
80n2:11 | Reactive Power Guard Min Error | Lower limit value for a reactive power error message [var] | REAL32 | RW | 0.000000 (0.000000e+000) |
80n2:12 | Reactive Power Guard Min Warning | Lower limit value for a reactive power warning message [var] | REAL32 | RW | 0.000000 (0.000000e+000) |
80n2:13 | Reactive Power Guard Max Warning | Upper limit value for a reactive power warning message [var] | REAL32 | RW | 230.000000 (2.300000e+002) |
80n2:14 | Reactive Power Guard Max Error | Upper limit value for a reactive power error message [var] | REAL32 | RW | 241.500000 (2.415000e+002) |
Index F800 DPM Settings
F800:0 | DPM Settings | Max. subindex | UINT8 | RO | 0x11 (17dec) |
F800:11 | Inaccurate Threshold | Limit value for the warning bit: DPM Inaccurate (Index 60n0:0B) | REAL32 | RW | 1.000000 (1.000000e+000) |