Power measurement at a machine
WARNING
WARNING: Risk of electric shock!
Bring the Bus Terminal system into a safe, voltage-free state before starting mounting, disassembly or wiring of the Bus Terminals!
Notice
Attention! Risk of device damage!
Avoid confusing the current and voltage circuit during connection, since the direct connection of mains voltage to the terminal points for the current transformers (typical input resistance 100 mΩ) would destroy the power measurement terminal!
EL3443
Power measurement at a machine 1:Fig.178: EL3443, power measurement at a machine
Power measurement at a machine 2:
Fuse protection of the terminal
The voltage measurement inputs L1 - L3 are high-impedance; a minimum measurement current flows. The fuses to the connection points L1 - L3 are therefore only to be designed according to the connection cross-section.
For the current measurement inputs IL1 – IL2, the fuse protection must be adapted according to the device to be measured.
The secondary currents of the transformers are not fused, see figure.
Power measurement at a machine 3:
**) FE as star point for 3-phase systems without neutral line
Depending on the current transformers used, FE must be connected as star point in 3‑phase systems without neutral line as shown in Fig. “EL3443, power measurement at a machine".
Observe the regulations of the manufacturer of the current transformers!
Power measurement at a machine 4:
Negative power values
If negative power values are measured on a circuit, please check whether the associated current transformer circuit is connected correctly.
EL3453
Power measurement at a machine 5:Fig.179: EL3453, power measurement at a machine
Power measurement at a machine 6: