EL3453-0090 - Technical data
Analog specifications
EL3453-0090
Number of inputs
4 x current, 3 x voltage
Technology
3-phase power measurement
Special feature
TwinSAFE Single Channel
Oversampling factor
Internal sampling rate
approx. 9.7 ksps (per channel)
Sampling type
simultaneously across all channels
Ground reference
single-ended
Update time
with each half-wave (10 ms at 50 Hz)
Parameters measured
EL3453-0090
Measured values
Current, voltage, active power, reactive power, apparent power, active energy, reactive energy, apparent energy, fundamental power and energy, cos φ, frequency, THD, harmonics (up to the 63rd harmonic), power quality factor (PowerQualityFactor)
Measuring error
0.3 % relative to full scale value (U/I), 0.6 % calculated values
Measuring procedure
true RMS value calculation
Nominal voltage range (mains voltage)
AC: 400 Vrms (ULX-N) or 690 Vrms (ULX-ULY) (TN network: 600 Vrms)
DC: 480 V with connection via L1 and L2 (or L3)
Technical voltage measuring range
520 Vrms (ULX-N) or 897 Vrms (ULX-ULY) common reference potential N/GND
max. time for voltages above 500 Vrms (ULX-N) or 863 Vrms (ULx-ULy): tmax < 10 s **)
Max. permitted overvoltage
max. ±736 V (peak value, ULX-N, equivalent to 520 Vrms) or max. ±1270 V (peak value, ULX-ULY, equivalent to 897 Vrms) **)
Internal resolution
24 bit
Input resistance voltage circuit
typ. 1.5 MΩ
Nominal current range
corresponding to AC:100 mArms;1 Arms (default);
5 Arms recommended via measuring transformer x A AC/1 A AC
Technical current measuring range
2.25 A (peak value, equivalent to 1.59 Arms) or 9.6 A (peak value, equivalent to 6.8 Arms)
Permissible overcurrent
max. ±10 A peak value, equivalent to 7 Arms **) per channel and
max. sum current (I1+I2+I3+IN) ±20 A peak value, equivalent to 14 Arms **)
Short-time current carrying capacity
60 A (sinusoidal) for 1 sec., the upstream use of current-limiting current transformers is recommended
Largest short-term deviation during a specified electrical interference test
< ±0.5 % of full scale value for the current measurement
Input resistance current circuit
typ. 3 mΩ
Frequency range
15 … 400 Hz***)
Cut-off frequency
4000 Hz
CAUTION
**) Consequences of prolonged operation above the nominal range of the measuring voltage
Prolonged operation above the nominal range can lead to functional impairment and/or shortening of the service life.
EL3453-0090 - Technical data 1:
***) Frequency measurement EL3453-0090
The time source for the frequency measurement has a stability of 100 ppm or better. The accuracy of the frequency measurements with a constant 50 Hz voltage signal is 5 mHz or more.
Supply and potentials
EL3453-0090
Electrical isolation
4500 V
Current consumption of power contacts
Current consumption via E-bus
260 mA typ.
Communication
EL3453‑0090
Configuration
via TwinCAT System Manager
Distributed clocks
optional (for determining the zero crossing time)
Accuracy of Distributed Clocks
<< 1 µs
Environmental conditions
EL3453-0090
perm. ambient temp.
range during operation
0 °C ... +55 °C
perm. ambient temp.
range during storage
-25 °C ... +85 °C
Relative humidity
95 %, no condensation
General data
EL3453-0090
MTBF (+55 °C)
> 1,148,000 h (equivalent to ~131 a)
Weight
approx. 100 g
Dimensions (W x H x D)
approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Installation position
variable
Standards and approvals
EL3453-0090
Vibration/shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity/emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Marking/certification*)
CE, EAC, UKCA