EL3453 - Technical data
Analog specifications | EL3453 | EL3453-0020 | EL3453-0100 | ||
Number of inputs | 4 x current, 3 x voltage | ||||
Technology | 3-phase power measurement | ||||
Special feature | - | factory calibrated with calibration certificate | - | ||
Oversampling factor | – | ||||
Internal sampling rate | approx. 9.7 ksps (per channel) | ||||
Sampling type | simultaneously across all channels | ||||
Ground reference | single-ended | ||||
Update time | with each half-wave (10 ms at 50 Hz) | ||||
Parameters measured | EL3453 | EL3453-0020 | EL3453-0100 |
Measured values | Current, voltage, active power, reactive power, apparent power, active energy, reactive energy, apparent energy, fundamental power and energy, cos φ, power factor, frequency, THD, harmonics (up to the 63rd harmonic), power quality factor (PowerQualityFactor) | ||
Measuring error | 0.3 % relative to full scale value (U/I), 0.6 % calculated values | ||
Accuracy class according to IEC 61557-12****) |
| in preparation | |
Measuring procedure | true RMS value calculation | ||
Nominal voltage range (mains voltage) | AC: 400 Vrms (ULX-N) or 690 Vrms (ULX-ULY) (TN network: 600 Vrms) DC: 480 V with connection via L1 and L2 (or L3) | corresponding to AC: | |
Technical voltage measuring range | 80-520 Vrms (ULX-N) or 139-897 Vrms (ULX-ULY) common reference potential N/GND max. time for voltages above 500 Vrms (ULX-N) or 863 Vrms (ULx-ULy): tmax < 10 s **) | 145 Vrms (ULX-N) common reference potential N/GND | |
Max. permitted overvoltage | max. ±736 V (peak value, ULX-N, equivalent to 520 Vrms) or max. ±1270 V (peak value, ULX-ULY, equivalent to 897 Vrms) **) | max. 300 Vrms (ULX-N) **) | |
Internal resolution | 24 bit | ||
Input resistance voltage circuit | typ. 1.5 MΩ | ||
Nominal current range | corresponding to AC:100 mArms;1 Arms (default); | ||
Technical current measuring range | 2.25 A (peak value, equivalent to 1.59 Arms) or 9.6 A (peak value, equivalent to 6.8 Arms) | ||
Permissible overcurrent**) | max. ±10 A peak value, equivalent to 7 Arms **) per channel and | ||
Short-time current carrying capacity | 60 A (sinusoidal) for 1 sec., the upstream use of current-limiting current transformers is recommended | ||
Largest short-term deviation during a specified electrical interference test | < ±0.5 % of full scale value for the current measurement | ||
Input resistance current circuit | typ. 3 mΩ | ||
Frequency range***) | 15 … 400 Hz | ||
Cut-off frequency | 4000 Hz | ||
**) Consequences of prolonged operation above the nominal range of the measuring voltage Prolonged operation above the nominal range can lead to functional impairment and/or shortening of the service life. |
![]() | ***) Frequency measurement EL3453 The time source for the frequency measurement has a stability of 100 ppm or better. The accuracy of the frequency measurements with a constant 50 Hz voltage signal is 5 mHz or more. |
Supply and potentials | EL3453 | EL3453-0020 | EL3453-0100 |
Electrical isolation | 4500 V | ||
Current consumption of power contacts | – | ||
Current consumption via E-bus | 260 mA typ. | ||
Communication | EL3453 | EL3453-0020 | EL3453-0100 |
Configuration | via TwinCAT System Manager | ||
Distributed clocks | optional (for determining the zero crossing time) | ||
Accuracy of Distributed Clocks | << 1 µs | ||
Environmental conditions | EL3453 | EL3453-0020 | EL3453-0100 |
perm. ambient temp. | -25 °C ... +60 °C | 0 °C ... +55 °C | |
perm. ambient temp. | -40 °C ... +85 °C | -25 °C ... +85 °C | |
Relative humidity | 95 %, no condensation | ||
General data | EL3453 | EL3453-0020 | EL3453-0100 |
Weight | approx. 100 g | ||
Dimensions (W x H x D) | approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm) | ||
on 35 mm mounting rail, conforms to EN 60715 | |||
Installation position | variable | ||
Standards and approvals | EL3453 | EL3453-0020 | EL3453-0100 |
Vibration/shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | ||
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 | ||
Protection rating | IP20 | ||
Marking/certification*) | CE, EAC, UKCA, cULus | ||