UL notice
![]()  | Application Beckhoff EtherCAT modules are intended for use with Beckhoff’s UL Listed EtherCAT System only.  | |
![]()  | Examination For cULus examination, the Beckhoff I/O System has only been investigated for risk of fire and electrical shock.  | |
![]()  | For devices with Ethernet connectors Not for connection to telecommunication circuits.  | |
Special conditions for intended use
- 1. For use with Listed current transformers suitably rated for the application only, terminals EL3453 and EL3783 may also measure the current directly.
 - 2. Connected wires must be rated min. 75°C, 300 V or 600 V (depends on rated voltage of EtherCAT Terminal) and be made of copper.
 - 3. If the equipment is used in a manner not specified by the manufacturer, the protection provided by the equipment may be impaired.
 - 4. Pollution degree 2.
 - 5. Requirements related to the external current transformers as per annex DVE of UL/CSA 61010-1:
- Per DVE.3.2.1:
 - Always open or disconnect circuit from power-distribution system (or service) of building before installing or servicing current transformers.
 - The current transformers may not be installed in equipment where they exceed 75 percent of the wiring space of any cross-sectional area within the equipment.
 - Restrict installation of current transformer in an area where it would block ventilation openings.
 - Restrict installation of current transformer in an area of breaker arc venting.
 - Not suitable for Class 2 wiring methods and not intended for connection to Class 2 equipment.
 - Secure current transformer and route conductors so that the conductors do not directly contact live terminals or bus.