Technical data
Technical data | EL3433 |
Measured values | Current, voltage, effective power, apparent power, frequency |
Calculated values | Reactive power, energy, power factor (cosφ), harmonic frequencies, phase angle |
Measuring voltage | max. 500 V AC 3~ (ULX-N: max. 288 V AC) |
Fed-in voltages must comply with overvoltage category II | |
Measuring current | max. 10 A (AC) (configurable) |
Input resistance voltage circuit (typ.) | 1 MΩ |
Input resistance current circuit (typ.) | < 3 mΩ |
Fuse protection | Voltage circuit: according to the connected conductor size Current circuit: primary side of the current transformer, according to the connected conductor size |
Resolution | 1 µA, 0.1 mV, 10 mW |
Measuring accuracy | 0.5% in relation to the full scale value (U/I) (at 0°C…55°C) 1% calculated value (P) Notice: |
Frequency range | 45 Hz to 65 Hz |
Signal type | any (taking into account the frequency range and the limit frequency) |
Measuring procedure | True RMS calculation with 16,800 (2,800 per channel) samples/s |
Sampling type | simultaneous |
Ground reference | single ended |
Measuring cycle time | 200 ms per measured value preset, freely configurable, mains-synchronous |
Electrical isolation | 4500 V (connection terminal/E-bus) |
Supply voltage for electronic | via the E-bus |
E-Bus current consumption | 200 mA typ. |
Configuration | via TwinCAT System Manager |
Dimensions (W x H x D) | approx. 27 mm x 100 mm x 70 mm (width aligned: 24 mm) |
Weight | approx. 100 g |
Mounting | on 35 mm mounting rail conforms to EN 60715 |
Operating temperature | -25 °C ... +60 °C (extended temperature range) |
Storage temperature | -40 °C ... +85 °C |
Relative humidity | 95 % no condensation |
Vibration/shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 |
Protect. class / installation pos. | IP20/any |
Marking / Approval*) | CE, UKCA, EAC |