Technical data
Technical data
EL3475
Number of inputs
12
Wiring
2-wire
Oversampling factor
Distributed clocks
optional (required for distributed power measurement)
Update interval
RMS values 20 ms at 50 Hz and 100 ms for other values such as harmonics
Measured values
current (with SVL or via DPM: voltage, active power, reactive power, apparent power, active energy, reactive energy, apparent energy, cos φ, frequency, THD, power quality factor, harmonics (up to the 50th harmonic))
Measuring voltage
via SVL
Measuring current
via SCL
Nominal voltage measurement range
333 mV RMS
Technical voltage measuring range
+/- 600 mV for 125 % overrange
Maximum permissible time for voltages above +/- 460 mV
tmax < 10 s**
Max. permitted overvoltage
+/- 1 V, above this voltage damage to the device cannot be ruled out
Measuring error
current: 0.3 % (relative to full scale value)
calculated values: 0.6 %
Update time
mains-synchronous
Monitoring functions
undercurrents/overcurrents (adjustable)
Electrical isolation
2500 V (channel/bus)
Current consumption via E-bus
typ. 150 mA
Current consumption from the power contacts
Special features
distributed power measurement (DPM), electronic nameplates can be read out
Width in the process image
configurable
default: 418 bytes input, 32 bytes output
Permissible ambient temperature range during operation
-25 °C ... +60 °C
Permissible ambient temperature range during storage
-40 °C ... +85 °C
Permissible relative air humidity
95 %, no condensation
Weight
approx. 75 g
Dimensions (W x H x D)
approx. 24 mm x 100 mm x 52 mm
Installation
on 35 mm DIN rail, conforms to EN 60715
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Approvals / markings*
CE, UKCA, EAC
Notice
**) Consequences of prolonged operation above the nominal range of the measuring voltage
Prolonged operation above the nominal range can lead to functional impairment and/or shortening of the service life.