EL3351 - LEDs and connection
EL3351 - LEDs and connection 1:Fig.27: Connection EL3351
EL3351 - LEDs
LED
Color
Meaning
RUN 1
RUN 2
green
These LEDs indicate the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set
single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
flickering
State of the EtherCAT State Machine: BOOTSTRAP = function for firmware updates of the terminal
ERROR 1
red
Range violation of the signal voltage UD or wire break
ERROR 2
red
Range violation of the reference voltage Uref
EL3351 - Connection
Terminal point
No.
+UD
1
+ input measuring voltage
-UD
2
- input measuring voltage
- UV
3
0 V (supply voltage)
Shield
4
Shield
+ UREF
5
+ input reference voltage
- UREF
6
- input reference voltage
+UV
7
+5 V (supply voltage)
Shield
8
Shield
Electrical isolation of the inputs
EL3351 - LEDs and connection 2:Fig.28: Electrical isolation of the inputs
EL3351 wiring
EL3351 - LEDs and connection 3:Fig.29: EL3351 wiring
The supply voltage UV can be drawn from the terminal or can be supplied from an external source. The terminal supplies 5 V. The maximum input voltage UREF is limited to 12 V.