Filter (conversion times)
The EL331x terminals are equipped with the following digital filters, cf. the data flow in chapter Data processing
Filter behavior
Example IIR low-pass 100 Hz:
Filter (conversion times) 1:Fig.267: Example IIR low-pass 100Hz
The notch filters attenuate the designated frequency and multiples thereof, here using the example 50 Hz FIR,
Typical curve of a notch filter set to 50 Hz:
Filter (conversion times) 2:Fig.268: Example notch filter
Conversion time/update rate from filter 1 (ADC filter)
The conversion time is dependent on the following:
Active channels * Number of measurements * Filter period + Calculation time = Conversion time
Example: EL3311 (1 channel), 3 measurements (thermocouple, wire break, cold junction), filter 50 Hz
1 channel * 3 measurements * (1/50 Hz) + 3 ms ≈ 63 ms
Example: EL3314 (2 channels), 3 measurements (thermocouple, wire break, cold junction), filter 50 Hz
2 channels * 3 measurements * (1/50 Hz) + 6 ms ≈ 126 ms
Example: EL3314 (4 channels), 3 measurements (thermocouple, wire break, cold junction), filter 50 Hz
4 channels * 3 measurements * (1/50 Hz) + 12 ms ≈ 252 ms
Typical conversion times with 3 measurements (thermocouple, wire break, cold junction)
Conversion times in relation to the filter frequencies:
Conversion time (update time)
Filter frequency
EL3311
EL3312
EL3314
EL3314-0010
EL3314-0030
EL3318
5 Hz
0.6 s
1.2 s
2.4 s
1.6 s
3.5 s
10 Hz
0.3 s
0.6 s
1.2 s
800 ms
1.75 s
50 Hz
63 ms
126 ms
250 ms
165 ms
380 ms
60 Hz
53 ms
106 ms
210 ms
145 ms
320 ms
100 Hz
33 ms
66 ms
130 ms
86 ms
200 ms
500 Hz
9 ms
18 ms
33 ms
26 ms
70 ms
1000 Hz
6 ms
12 ms
24 ms
18 ms
50 ms
2000 Hz
5 ms
10 ms
20 ms (14 from FW10)
14 ms
40 ms
3750 Hz
4 ms
8 ms
19 ms (12 from FW10)
12 ms
35 ms
7500 Hz
4 ms
7 ms
19 ms (10 from FW10)
12 ms
30 ms
15000 Hz
3 ms
7 ms
19 ms (9 from FW10)
12 ms
30 ms
30000 Hz
3 ms
7 ms
19 ms (8 from FW10)
12 ms
30 ms
mV range
3 ms
6 ms
12 ms
12 ms
25 ms
Conversion times in relation to the filter frequencies, EL3314-0002 (from FW02), EL3314-0092:
Filter frequency
EL3314-0002, EL3314-0092
50/60 Hz
114 ms
2.5 Hz
2400 ms
5 Hz
1200 ms
10 Hz
600 ms
16.6 Hz
360 ms
20 Hz
300 ms
50 Hz
122 ms
60 Hz
102 ms
100 Hz
62 ms
200 Hz
31 ms
400 Hz
17 ms
800 Hz
10 ms
1000 Hz
8 ms
2000 Hz
5 ms
4000 Hz
4 ms
mV range
4 ms
Conversion time from filter 2 (MC filter)
If available, the MC filter can further attenuate the temperature value. The final conversion rate results from the conversion time set in the ADC (table in previous section) and the MC setting according to
FFilter frequency final [Hz] = 1 / (k * tconversion time ADC)
with k as measure for the signal rise up to 70% (-3 dB) after
Filter designation
k
Behavior
FIR4
3
Notch filter behavior
FIR8
6
FIR16
12
FIR32
23
IIR0
2
Low-pass behavior
IIR1
5
IIR2
10
IIR3
19
Example: for the EL3314-0010 with ADC filter 50 Hz (thus 166 ms according to the above table) and FIR16 results in FFilter frequency final = 1 / (12 * 166 ms) = 0.5 Hz.