Connection instructions for earthed/potential-free thermocouples
Due to the differential inputs of the terminals, different connection types are recommended depending on the type of thermocouple used. For earthed thermocouples, ground is not connected to the shielding. If the thermocouple does not have an ground connection, the ground and shielding contacts can be connected (see Fig. Connection of earthed and earth-free thermocouples and Connection instructions for thermocouples).
Connection instructions for earthed/potential-free thermocouples 1:
  • Earthed thermocouple
  • Do not connect GND to the shielding
  • For EL3312: potential difference max. 2 V
  • Potential-free / earth-free thermocouple
  • GND can be connected to the shielding
  • or: GND can connected to any potential, max. 35 V to 0 V power
  • Non-potential-free thermocouple
  • Do not connect GND to thermocouple potential.
  • Thermocouple-potential max. 35 V to 0 V power
  • For different thermocouple potentials several 1-channel EL3311 units should be used.
  • Unused inputs
  • For the multi-channel versions EL3312, EL3314 and EL3318 unused inputs should be short-circuited (low-resistance connection of +TC, -TC)
    Unused high-resistance inputs can affect the EMC of the terminal and thus influence the channels used.
    Unused channels can also generate unwanted waste heat.
Connection instructions for earthed/potential-free thermocouples 2:Fig.140: Connection methods for earthed and earth-free thermocouples
The example shows EL3312. For the EL3314, the shield should be connected to an additional shield terminal (EL9195).