Notch filter
The EL32xx terminals are equipped with a digital filter. The filter performs a notch filter function and determines the conversion time of the terminal. It is parameterized via the index 0x8000:15. The higher the filter frequency, the faster the conversion time.
Notch filter means that the filter has zeros (notches) in the frequency response at the specified filter frequency and multiples thereof, i.e. it masks these frequencies. In order to filter out 50 Hz, therefore, the 50 or the 10 Hz filter can be used. Since all frequencies lower than the notch frequency usually have to be measured, however, the "50 Hz" setting is to be used in this case.
![]() | Index 0x80n00:06 The filter function is always active even if the bit is not set, since this is obligatory for the measurement process! The firmware filter can therefore not be switched off. |
Details on the conversion time
- The conversion time depends on the number of active channels, number of measurements (2/4-wire), filter time, const. computing time
- The conversion time for the 2-wire measurement is about twice as long as for the 4-wire measurement
- The resistance measurement corresponds to a 4-wire measurement
- The process data TxPDO Toggle changes its state if a new measured value is present
![]() | The filter characteristics are set via index 0x8000:15 The filter frequencies are set centrally for all channels of the EL32xx terminals via index 0x8000:15 (channel 1). The corresponding indices 0x8010:15 of the EL3202 or 0x8010:15, 0x8020:15, 0x8030:15 of the EL3204 have no parameterization function. |
![]() | Switching off the unused channels of multi-channel terminals Unused channels should be switched off by "not connected" if filter frequencies are ≥ 1 kHz (optimization of conversion times)! |
By means of a double click on the corresponding object 0x80n0:1A, the respective channels can be switched off in the Set Value Dialog by selecting the "Enum" value "not connected" (see fig. "Set Value Dialog").
![]() | Interference from equipment When operating the fast analog EL320x EtherCAT terminals, high frequency superimposed signals from interfering devices (e.g. proportional valves, stepper motors or DC motor output stages) can be picked up by the terminal.
Typical conversion times
EL3201, EL3201-0010, EL3201-0020, EL3201-0030
Filter frequency | Conversion time (update time) |
5 Hz | 205 ms |
10 Hz | 105 ms |
50 Hz | 25 ms |
60 Hz | 21 ms |
100 Hz | 15 ms |
500 Hz | 5 ms |
1000 Hz | 4 ms |
2000 Hz | 4 ms |
3750 Hz | 4 ms |
7500 Hz | 4 ms |
15000 Hz | 4 ms |
30000 Hz | 4 ms |
Conversion times in relation to the filter frequencies, 4-wire measurement | |
EL3202
5 Hz | 807 ms |
10 Hz | 410 ms |
50 Hz | 88 ms |
60 Hz | 75 ms |
100 Hz | 46 ms |
500 Hz | 13 ms |
1000 Hz | 10 ms |
2000 Hz | 7 ms |
3750 Hz | 6 ms |
7500 Hz | 5 ms |
15000 Hz | 5 ms |
30000 Hz | 5 ms |
Conversion times in relation to the filter frequencies, 3-wire measurement | |
EL3202-0010, EL3202-0020, EL3202-0030
Filter frequency | Conversion time (update time) | |
4-wire update rate | 3-wire update rate | |
5 Hz | 410 ms | 610 ms |
10 Hz | 210 ms | 310 ms |
50 Hz | 47 ms | 67 ms |
60 Hz | 40 ms | 57 ms |
100 Hz | 25 ms | 35 ms |
500 Hz | 7 ms | 10 ms |
1000 Hz | 5 ms | 7 ms |
2000 Hz | 4 ms | 5 ms |
3750 Hz | 4 ms | 5 ms |
7500 Hz | 4 ms | 5 ms |
15000 Hz | 4 ms | 5 ms |
30000 Hz | 4 ms | 5 ms |
EL3204
5 Hz | 800 ms |
10 Hz | 400 ms |
50 Hz | 82 ms (21 ms / 1 channel) |
60 Hz | 70 ms |
100 Hz | 43 ms |
500 Hz | 11 ms |
1000 Hz | 7 ms |
2000 Hz | 6.5 ms (2 ms / 1 channel) |
3750 Hz | 6 ms |
7500 Hz | 6 ms |
15000 Hz | 6 ms |
30000 Hz | 6 ms |
EL3208
1 channel active | 8 channels active | |
5 Hz | 201 ms | 1600 ms |
10 Hz | 101 ms | 807 ms |
50 Hz | 22 ms | 171 ms |
60 Hz | 18 ms | 145 ms |
100 Hz | 12 ms | 92 ms |
500 Hz | 4 ms | 29 ms |
1000 Hz | 3 ms | 20 ms |
2000 Hz | 3 ms | 20 ms |
3750 Hz | 3 ms | 20 ms |
7500 Hz | 3 ms | 20 ms |
15000 Hz | 3 ms | 20 ms |
30000 Hz | 3 ms | 20 ms |
Conversion times in relation to the filter frequencies, 2-wire measurement | ||
EL3214 and EL3218
1 channel active | 4 channels active | |
5 Hz | 402 ms | 1607 ms |
10 Hz | 203 ms | 811 ms |
50 Hz | 44 ms | 175 ms |
60 Hz | 37 ms | 148 ms |
100 Hz | 24 ms | 95 ms |
500 Hz | 8 ms | 32 ms |
1000 Hz | 6 ms | 24 ms |
2000 Hz | 6 ms | 22 ms |
3750 Hz | 5 ms | 21 ms |
7500 Hz | 5 ms | 20 ms |
Conversion times in relation to the filter frequencies, 3-wire measurement | ||