Technical data
Technical data
EL3255
Number of inputs
5
Power supply
via power contacts
Technology
Ratiometric potentiometer evaluation with own supply, 3-wire connection
Distributed Clocks
yes
Feed voltage potentiometer
typ. 10 V ±10%
Internal resistance
>> 100 kΩ to wiper connection
Sensor types
Potentiometer 300 Ω…50 kΩ
Output current
max. 0.3 A total supply current for the potentiometer
Input filter limit frequency
typ. - 3 dB at 3 kHz and potentiometer 50 kOhm
Wiring fail indication
yes
Conversion time
typ. 300..700 µs, depending on settings
Default: approx. 500 µs (5 channels, filter deactivated)
Resolution
16 bits (including sign)
Sampling type
simultaneous
Ground reference
single-ended
Measuring error
< ±0.5 % (relative to full scale value)
Voltage supply for electronic
via the E-bus
Special features
open-circuit recognition, supply monitoring, activatable filters, simultaneous measurement of channels
Electrical isolation
500 V (E-bus/field voltage)
Current consumption of power contacts (supply contacts)
depends on potentiometers, max. 70 mA
Current consumption via E-bus
typ. 80 mA
Bit width in the process data image
5 x 16 bit input
Configuration
no address setting, configuration via the controller
Conductor connection
solid wire conductors: direct plug-in technique;
stranded wire conductors and ferrules: spring actuation by screwdriver
Rated cross-section
solid wire: 0.08…1.5 mm²; stranded wire: 0.25...1.5 mm²; ferrule: 0.14…0.75 mm²
Max. Sensor cable length
The cable length from the EtherCAT Terminal to the sensor/encoder must not exceed 30 m without further protective measures. Suitable surge protection must be provided for longer cable lengths
Weight
approx. 70  g
Permissible ambient temperature range during operation
-25°C ... +60°C (extended temperature range)
Permissible ambient temperature range during storage
-40°C ... +85°C
Permissible relative humidity
95%, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm
Mounting
on 35 mm mounting rail conforms to EN 60715
Vibration/shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27,
see also installation instructions for enhanced mechanical load capacity
EMC immunity/emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP20
Installation position
variable
Marking / Approval*)
CE, UKCA, EAC
ATEX, IECEx
cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex nA IIC T4 Gc
IECEx
Ex nA IIC T4 Gc