Operating modes
The EL30xx and the EL31xx accordingly supports three different operating modes: “Freerun” (filter on, timer interrupt), “Synchron” (filter off, SyncManager interrupt) and “DC” (DC Sync interrupt)
Operating modes 1:Fig.224: Relationship of operating modes
The terminal switches between the “Freerun” (filter on) and Synchron modes by activating/deactivating the filter via the index. The terminal remains in OP mode during this process. The changeover may result in longer sampling times and step changes in the process data until the filters have assumed a steady state.
DC mode can only be used when the filters are switched off. Likewise, it is not possible to switch the filters on in DC mode. The DC mode is parameterized via the “DC” tab in the TwinCAT System Manager.
The operating modes of the EL30xx/EL31xx are:
Mode
1 (default)
2
3
4
5
6
Filter (Index: 0x8000:06)
On (default.: 50 Hz FIR)
Off
Distributed Clocks mode
Off
On
Possible with EL30xx
x
x
x
x
x
Possible with EL31xx
x
x
x
x
x
x
Default setting for
EL30xx
EL31xx
Synchronization mode (index:0x1C33:01, bit 0+1)
0: FreeRun (default)
1: Frame triggered (SM3 inputs)
3: DC mode
FastOp-Mode "CoE" (Index: 0x1C33:01, bit 15)
Off (default)
Off (default)
On
Off (default)
On
Off (default)
(FastOP mode n.a. in DC mode)
StartUp entry index 0x1C33:01
0x0000
0x0000
0x8000
0x0001
0x8001
Update frequency
depends on filter setting; automatically set inside the terminal
see following values
EtherCAT cycle time, if value does not fall below the lower setting-dependent limit. See following values for typical limit.
Operation with a faster EtherCAT cycle is possible, but in that case the EL30xx no longer supplies new data in each cycle.
typical data update time (EL30x1)
50 Hz FIR: typical 625 µs
60 Hz FIR: typical 520 µs
IIR: typical 1 ms
< 600 µs
< 500 µs
typ. data update time (EL30x2)
typ. data update time (EL30x4)
typ. data update time (EL30x8)
50 Hz FIR: typ. 1.25 ms
60 Hz FIR: typ. 1 ms
IIR: typ. 1 ms
< 1.1 ms
< 1 ms
Note
If filtering is enabled, the following settings are activated in the EL30xx,
irrespective of other settings
“FreeRun” = on
and
“FastOp mode” = off.
The notes on the minimum EtherCAT cycle time in DC mode must be observed.
Operating modes 2:
Combinations of filters, FastOp mode and Synchronization mode
Other combination options of filter, FastOp mode and Synchronization mode are expressly not recommended.
Synchron mode
In synchronous operation process data are generated frame-triggered, so that a new value is available with each PLC cycle. In the EL31xx terminals synchron mode is used automatically (filter off, no DC). The minimum cycle times are 80 µs (EL31x1/EL31x2), and 120 µs (EL31x4) for standard IPCs.
DC operation
In DC mode the process data are requested via DC interrupt. This results in the temporal jitter between two frames being equalized, so that the sampling time is uniform across the system.
The EL31xx should be operated in DC input based mode.
The DC mode requires minimum cycle times of
for standard IPCs.
In input-based mode the sync interrupt is shifted automatically, so that the process data are ready just before the current process data cycle.
If the frame jitter is too large, there is still the possibility that duplicate data will be retrieved or that the transmission will be interrupted. Then the jitter must be reduced or a slower cycle time selected by TwinCAT system corrective measures.