EL3174-0030 - Connection, display and diagnostics
Fig.48: EL3174-0030 - LEDs and ConnectionConnection EL3174-0030 | ||||
Terminal point | Description | Internally connected | Max. current carrying capacity *) | |
Name | No. | |||
Ch1 U+ | 1 | Channel 1, voltage measurement, positive input (U+) | - | not applicable (voltage input) |
Ch2 U+ | 2 | Channel 2, voltage measurement, positive input (U+) | - | not applicable (voltage input) |
Ch3 U+ | 3 | Channel 3, voltage measurement, positive input (U+) | - | not applicable (voltage input) |
Ch4 U+ | 4 | Channel 4, voltage measurement, positive input (U+) | - | not applicable (voltage input) |
+24 V | 5, 6, 7, 8 | +24 V | positive power contact | 1 A |
Ch1 U- | 9 | Channel 1, voltage measurement, negative input (U-) | - | not applicable (voltage input) |
Ch2 U- | 10 | Channel 2, voltage measurement, negative input (U-) | - | not applicable (voltage input) |
Ch3 U- | 11 | Channel 3, voltage measurement, negative input (U-) | - | not applicable (voltage input) |
Ch4 U- | 12 | Channel 4, voltage measurement, negative input (U-) | - | not applicable (voltage input) |
Input Ch1 | 13 | Channel 1, current measurement, input (I) | - | 40 mA |
Input Ch2 | 14 | Channel 2, current measurement, input (I) | - | 40 mA |
Input Ch3 | 15 | Channel 3, current measurement, input (I) | - | 40 mA |
Input Ch4 | 16 | Channel 4, current measurement, input (I) | - | 40 mA |
*) Constant and peak value | ||||
![]() | Overcurrent protection of the 20 mA inputs The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
LEDs | |||
LED | Color | Meaning | |
RUN* | green | This LED indicates the terminal's operating state *: | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set | ||
single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
ERROR** | red | Fault indication in the event of broken wire or undershooting or overshooting of the measuring range | |
*) If several RUN LEDs are present, all of them have the same function. | |||