EL3174-0002 - Connection, display and diagnostics
EL3174-0002 - Connection, display and diagnostics 1:Fig.74: EL3174-0002 - LEDs and connection
EL3174-0002 connection
Terminal point
Internally connected with connection
Max. current carrying capacity *)
No.
+ Input 1
1
Channel 1, voltage/current measurement (U/ I), positive input (+)
40 mA
+ Input 2
2
Channel 2, voltage/current measurement (U/ I), positive input (+)
40 mA
+ Input 3
3
Channel 3, voltage/current measurement (U/ I), positive input (+)
40 mA
+ Input 4
4
Channel 4, voltage/current measurement (U/ I), positive input (+)
40 mA
- Input 1
5
Channel 1, voltage/current measurement (U/ I), negative input (-)
40 mA
- Input 2
6
Channel 2, voltage/current measurement (U/ I), negative input (-)
40 mA
- Input 3
7
Channel 3, voltage/current measurement (U/ I), negative input (-)
40 mA
- Input 4
8
Channel 4, voltage/current measurement (U/ I), negative input (-)
40 mA
*) Constant and peak value
EL3174-0002 - Connection, display and diagnostics 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
  • In the event of a fault, the current limiter must not be overloaded by a voltage > 30 V from the source device.
  • Overcurrent is displayed in the process image as "Overrange".
  • After occurrence, the error condition must be stopped immediately, the source device switched off or disconnected from the input terminal.
  • If the error condition persists for a longer period of time, the internal terminal current limitation reduces the absorbed signal current for thermal reasons, depending on the ambient conditions also below 20 mA.
EL3174-0002 LEDs
EL3174-0002 - Connection, display and diagnostics 3:Fig.76: EL3174-0002 - LEDs
LED
Color
Meaning
RUN*
green
These LEDs indicate the terminal's operating state *:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
ERROR**
red
Error indication in the event of a wire break or when the measuring range is exceeded or not reached
*) If there are several RUN-LEDs, they all have the same function.