EL3174 - Connection, display and diagnostics
EL3174 - Connection, display and diagnostics 1:Fig.71: EL3174 - LEDs and connection
EL3174 connection
Terminal point
Internally connected
with connection
Max. current carrying capacity *)
Abbreviation
No.
Ch1 U+
1
Channel 1, voltage measurement, positive input (U+)
not applicable (voltage inputs)
Ch2 U+
2
Channel 2, voltage measurement, positive input (U+)
Ch3 U+
3
Channel 3, voltage measurement, positive input (U+)
Ch4 U+
4
Channel 4, voltage measurement, positive input (U+)
+24 V DC
5, 6, 7, 8
+24 V
positive power contact
1 A
Ch1 U-
9
Channel 1, voltage measurement, negative input (U-)
Ch2 U-
10
Channel 2, voltage measurement, negative input (U-)
Ch3 U-
11
Channel 3, voltage measurement, negative input (U-)
Ch4 U-
12
Channel 4, voltage measurement, negative input (U-)
Ch1 I-
13
Channel 1, current measurement, input (I)
40 mA
Ch2 I-
14
Channel 2, current measurement, input (I)
40 mA
Ch3 I-
15
Channel 3, current measurement, input (I)
40 mA
Ch4 I-
16
Channel 4, current measurement, input (I)
40 mA
*) Constant and peak value
EL3174 - Connection, display and diagnostics 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
  • In the event of a fault, the current limiter must not be overloaded by a voltage > 30 V from the source device.
  • Overcurrent is displayed in the process image as "Overrange".
  • After occurrence, the error condition must be stopped immediately, the source device switched off or disconnected from the input terminal.
  • If the error condition persists for a longer period of time, the internal terminal current limitation reduces the absorbed signal current for thermal reasons, depending on the ambient conditions also below 20 mA.
EL3174 LEDs
EL3174 - Connection, display and diagnostics 3:Fig.73: EL3174 - LEDs
LED
Color
Meaning
RUN*
green
These LEDs indicate the terminal's operating state *:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
ERROR**
red
Error indication in the event of a wire break or when the measuring range is exceeded or not reached
*) If there are several RUN-LEDs, they all have the same function.
**) The error display shows the signal processing state for each channel.