EL3154 - Connection, display and diagnostics
EL3154 connection
Terminal point | Description | Internally connected with connection | Max. current carrying capacity *) | |
Name | No. | |||
Input 1 | 1 | Input 1 | - | 40 mA |
+24 V | 2 | +24 V | 4, 6, 8 | 500 mA |
Input 3 | 3 | Input 3 | - | 40 mA |
+24 V | 4 | +24 V | 2, 6, 8 | 500 mA |
Input 2 | 5 | Input 2 | - | 40 mA |
+24 V | 6 | +24 V | 2, 4, 8 | 500 mA |
Input 4 | 7 | Input 4 | - | 40 mA |
+24 V | 8 | +24 V | 2, 4, 6 | 500 mA |
*) Constant and peak value | ||||
![]() | Overcurrent protection of the 20 mA inputs The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
EL3154 LEDs
LED | Color | Meaning | |
RUN* | green | These LEDs indicate the terminal's operating state *: | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set | ||
Single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
ERROR** | red | Error indication when the measuring range is exceeded or not reached | |
*) If there are several RUN-LEDs, they all have the same function. | |||
