EL3144 - Connection, display and diagnostics
EL3144 connection
Terminal point | Description | Internally connected with connection | Max. current carrying capacity *) | |
Name | No. | |||
Input 1 | 1 | Input 1 | - | 40 mA |
GND | 2 | Signal ground for input 1 | 4, 6, 8 | 40 mA |
Input 3 | 3 | + Input 3 | - | 40 mA |
GND | 4 | Signal ground for input 3 | 2, 6, 8 | 40 mA |
Input 2 | 5 | + Input 2 | - | 40 mA |
GND | 6 | Signal ground for input 2 | 2, 4, 8 | 40 mA |
Input 4 | 7 | + Input 4 | - | 40 mA |
GND | 8 | Signal ground for input 4 | 2, 4, 6 | 40 mA |
*) Constant and peak value | ||||
Notice | |
Terminal GND and system GND The signal ground GND of this terminal is not internally connected to the negative power contact. This design allows GND to be connected to a ground other than the negative power contact "Power contact 0V" if necessary. |
![]() | Overcurrent protection of the 20 mA inputs The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
EL3144 LEDs
LED | Color | Meaning | |
RUN* | green | These LEDs indicate the terminal's operating state *: | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set | ||
Single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
ERROR** | red | Error indication when the measuring range is exceeded or not reached | |
*) If there are several RUN-LEDs, they all have the same function. | |||