EL3142 - Connection, display and diagnostics
EL3142 - Connection, display and diagnostics 1:
EL3142 - LEDs and connection
Connection EL3142
Terminal point
Internally connected
with connection
Max. current carrying capacity *)
No.
+ Input 1
1
+ Input 1
40 mA
+24 V
2
+24 V
6, positive power contact
1 A
0 V
3
0 V
7, negative power contact
1 A
Shield
4
Shield (FE)
8; DIN rail
100 mA **)
+ Input 2
5
+ Input 2
40 mA
+24 V
6
+24 V
2, positive power contact
1 A
0 V
7
0 V
3, negative power contact
1 A
Shield
8
Shield (FE)
4; DIN rail
100 mA **)
*) Constant and peak value
**) Shield lines should be de-energized!
EL3142 - Connection, display and diagnostics 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30mA may occur. In the event of a fault, the current limiter must not be overloaded by a voltage > 30V from the source device.
Overcurrent is displayed in the process image as "Overrange". After occurrence, the error condition must be stopped immediately, the source device switched off or disconnected from the input terminal. If the error condition persists for a longer period of time, the internal terminal current limitation reduces the absorbed signal current for thermal reasons, depending on the ambient conditions also below 20 mA.
LEDs
LED
Color
Meaning
RUN*
green
This LED indicates the terminal's operating state *:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set
single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
ERROR**
red
Fault indication in the event of undershooting or overshooting of the measuring range
*) If several RUN LEDs are present, all of them have the same function
**) The error display shows the signal processing state for each channel
