EL3102 - Connection, display and diagnostics
Fig.6: EL3102 - LEDs and connectionConnection EL3102 | ||||
Terminal point | Description | Internally connected with connection | Max. current carrying capacity *) | |
Name | No. | |||
+ Input 1 | 1 | + Input 1 | - | not applicable (voltage input) |
- Input 1 | 2 | - Input 1 | - | not applicable (voltage input) |
GND | 3 | Signal ground for Input 1 | 7, (high impedance, therefore potential equal but not current loadable) | 40 mA |
Shield | 4 | Shield (FE) | 8; DIN rail | 100 mA **) |
+ Input 2 | 5 | + Input 2 | - | not applicable (voltage input) |
- Input 2 | 6 | - Input 2 | - | not applicable (voltage input) |
GND | 7 | Signal ground for Input 2 | 3, (high impedance, therefore potential equal but not current loadable) | 40 mA |
Shield | 8 | Shield (FE) | 4; DIN rail | 100 mA **) |
*) Constant and peak value | ||||
![]() | GND connection points The GND connection points of the terminal are not connected internally directly, but via EMC protection components. Therefore, each analog encoder/sensor must be connected separately with 2 wires, even if the connection diagram of the terminal for the channels indicates a common ground (GND). |
![]() | Current carrying capacity of the input contacts The maximum permitted current on the signal-relevant terminal points (inputs, GND) is 40 mA (if applicable). |
Notice | |
Terminal GND and system GND The signal ground GND of this terminal is not internally connected to the negative power contact. This design allows GND to be connected to a ground other than the negative power contact "Power contact 0V" if necessary. |
LEDs | |||
LED | Color | Meaning | |
RUN* | green | This LED indicates the terminal's operating state (if more than one RUN LED is present, all of them have the same function): | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set | ||
single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
*) If several RUN LEDs are present, all of them have the same function | |||