EL3101 - Connection, display and diagnostics
EL3101 - Connection, display and diagnostics 1:Fig.4: EL3101 - LED and connection
EL3101 connection
Terminal point
Internally connected with connection
Max. current carrying capacity *)
No.
+ Input 1
1
+ Input 1
not applicable (voltage input)
- Input 1
2
- Input 1
GND
3
Signal ground for input 1
7 (high-resistance, therefore potential equal but not current carrying)
40 mA
Shield
4
Shield (FE)
8, DIN rail
100 mA **)
n.c.
5
not connected
n.c.
6
not connected
GND
7
3 (high-resistance, therefore potential equal but not current carrying)
40 mA
Shield
8
Shield (FE)
4, DIN rail
100 mA **)
*) Constant and peak value
**) Shield lines should be de-energized!
EL3101 - Connection, display and diagnostics 2:
GND connection points
The GND connection points of the terminal are not connected internally directly, but via EMC protection components. Therefore, each analog encoder/sensor must be connected separately with 2 wires, even if the connection diagram of the terminal for the channels indicates a common ground (GND).
EL3101 - Connection, display and diagnostics 3:
Current carrying capacity of the input contacts
The maximum permitted current on the signal-relevant terminal points (inputs, GND) is 40 mA (if applicable).
Notice
Terminal GND and system GND
The signal ground GND of this terminal is not internally connected to the negative power contact. This design allows GND to be connected to a ground other than the negative power contact "Power contact 0V" if necessary.
If disturbing potential differences occur, GND must be electrically connected to the system GND or another suitable ground.
EL3101 LEDs
EL3101 - Connection, display and diagnostics 4:
EL3101 - LEDs
LED
Color
Meaning
RUN*
green
These LEDs indicate the terminal's operating state. If several RUN LEDs are present, all of them have the same function:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for terminal firmware updates
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different default settings set
Single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
*) If several RUN LEDs are present, all of them have the same function.