Standard objects
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: the Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x012C1389 (19665801dec) |
Index 1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL30xx |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
00 |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
01 |
Index 100B Bootloader version*)
100B:0B | Bootloader version | Bootloader version | STRING | RO | 00 |
*) from Firmware 20, Revision 0021
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0xXXXX3052 |
1018:03 | Revision | Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description | UINT32 | RO | - |
1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 | UINT32 | RO | - |
Index 10E2 Manufacturer-specific Identification Code*)
10E2:0 | Manufacturer-specific identification code | Manufacturer specific identification code | UINT8 | RO | 0x01 (1dec) |
10E2:01 | Subindex 001 |
| STRING | RO |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardised loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1800 AI TxPDO-Par Standard Ch.1
1800:0 | AI TxPDO-Par Standard Ch.1 | PDO parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1800:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 01 1A |
Index 1801 AI TxPDO-Par Compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1801:0 |
AI TxPDO-Par Compact Ch.1 |
PDO parameter TxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1801:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 |
OCTET-STRING[2] |
RO |
00 1A |
Index 1802 AI TxPDO-Par Standard Ch.2
1802:0 | AI TxPDO-Par Standard Ch.2 | PDO parameter TxPDO 3 | UINT8 | RO | 0x06 (6dec) |
1802:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3 | OCTET-STRING[2] | RO | 03 1A |
Index 1803 AI TxPDO-Par Compact Ch. 2
1803:0 | AI TxPDO-Par Compact Ch.2 | PDO parameter TxPDO 4 | UINT8 | RO | 0x06 (6dec) |
1803:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4 | OCTET-STRING[2] | RO | 02 1A |
Index 1804 AI TxPDO-Par Standard Ch.3
1804:0 | AI TxPDO-Par Standard Ch.3 | PDO parameter TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1804:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5 | OCTET-STRING[2] | RO | 05 1A |
Index 1805 AI TxPDO-Par Compact Ch. 3
1805:0 | AI TxPDO-Par Compact Ch.3 | PDO parameter TxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1805:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6 | OCTET-STRING[2] | RO | 04 1A |
Index 1806 AI TxPDO-Par Standard Ch.4
1806:0 | AI TxPDO-Par Standard Ch.4 | PDO parameter TxPDO 7 | UINT8 | RO | 0x06 (6dec) |
1806:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7 | OCTET-STRING[2] | RO | 07 1A |
Index 1807 AI TxPDO-Par Compact Ch. 4
1807:0 | AI TxPDO-Par Compact Ch.4 | PDO parameter TxPDO 8 | UINT8 | RO | 0x06 (6dec) |
1807:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8 | OCTET-STRING[2] | RO | 06 1A |
Index 1808 AI TxPDO-Par Standard Ch.5
1808:0 | AI TxPDO-Par Standard Ch.5 | PDO parameter TxPDO 9 | UINT8 | RO | 0x06 (6dec) |
1808:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 9 | OCTET-STRING[2] | RO | 09 1A |
Index 1809 AI TxPDO-Par Compact Ch. 5
1809:0 | AI TxPDO-Par Compact Ch.5 | PDO parameter TxPDO 10 | UINT8 | RO | 0x06 (6dec) |
1809:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 10 | OCTET-STRING[2] | RO | 08 1A |
Index 180A AI TxPDO-Par Standard Ch.6
180A:0 | AI TxPDO-Par Standard Ch.6 | PDO parameter TxPDO 11 | UINT8 | RO | 0x06 (6dec) |
180A:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 11 | OCTET-STRING[2] | RO | 0B 1A |
Index 180B AI TxPDO-Par Compact Ch.6
180B:0 | AI TxPDO-Par Compact Ch.6 | PDO parameter TxPDO 12 | UINT8 | RO | 0x06 (6dec) |
180B:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 12 | OCTET-STRING[2] | RO | 0A 1A |
Index 180C AI TxPDO-Par Standard Ch.7
180C:0 | AI TxPDO-Par Standard Ch.7 | PDO parameter TxPDO 13 | UINT8 | RO | 0x06 (6dec) |
180C:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 13 | OCTET-STRING[2] | RO | 0D 1A |
Index 180D AI TxPDO-Par Compact Ch.7
180D:0 | AI TxPDO-Par Compact Ch.7 | PDO parameter TxPDO 14 | UINT8 | RO | 0x06 (6dec) |
180D:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 14 | OCTET-STRING[2] | RO | 0C 1A |
Index 180E AI TxPDO-Par Standard Ch.8
180E:0 | AI TxPDO-Par Standard Ch.8 | PDO parameter TxPDO 15 | UINT8 | RO | 0x06 (6dec) |
180E:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 15 | OCTET-STRING[2] | RO | 0F 1A |
Index 180F AI TxPDO-Par Compact Ch.8
180F:0 | AI TxPDO-Par Compact Ch.8 | PDO parameter TxPDO 16 | UINT8 | RO | 0x06 (6dec) |
180F:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 16 | OCTET-STRING[2] | RO | 0E 1A |
Index 1A00 AI TxPDO-Map Standard Ch.1
1A00:0 | AI TxPDO-Map Standard Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x0A (10dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6000:03, 2 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6000:05, 2 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6000:07, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6000:11, 16 |
Index 1A01 AI TxPDO-Map Compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A01:0 |
AI TxPDO-Map Compact Ch.1 |
PDO Mapping TxPDO 2 |
UINT8 |
RO |
0x01 (1dec) |
1A01:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6000:11, 16 |
Index 1A02 AI TxPDO-Map Standard Ch.2
1A02:0 | AI TxPDO-Map Standard Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x0A (10dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6010:01, 1 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6010:02, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6010:03, 2 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6010:05, 2 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6010:07, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6010:0F, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A03 AI TxPDO-Map Compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A03:0 |
AI TxPDO-Map Compact Ch.2 |
PDO Mapping TxPDO 4 |
UINT8 |
RO |
0x01 (1dec) |
1A03:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6010:11, 16 |
Index 1A04 AI TxPDO-Map Standard Ch.3
1A04:0 | AI TxPDO-Map Standard Ch.3 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x09 (9dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6020:01, 1 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6020:02, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6020:03, 2 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6020:05, 2 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6020:07, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6020:0F, 1 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6020:10, 1 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6020:11, 16 |
Index 1A05 AI TxPDO-Map Compact Ch.3
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A05:0 |
AI TxPDO-Map Compact Ch.3 |
PDO Mapping TxPDO 6 |
UINT8 |
RO |
0x01 (1dec) |
1A05:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6020:11, 16 |
Index 1A06 AI TxPDO-Map Standard Ch.4
1A06:0 | AI TxPDO-Map Standard Ch.4 | PDO Mapping TxPDO 7 | UINT8 | RO | 0x0A (10dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6030:01, 1 |
1A06:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6030:02, 1 |
1A06:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6030:03, 2 |
1A06:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6030:05, 2 |
1A06:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6030:07, 1 |
1A06:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A06:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A06:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6030:0F, 1 |
1A06:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6030:10, 1 |
1A06:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6030:11, 16 |
Index 1A07 AI TxPDO-Map Compact Ch.4
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A07:0 |
AI TxPDO-Map Compact Ch.4 |
PDO Mapping TxPDO 8 |
UINT8 |
RO |
0x01 (1dec) |
1A07:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6030:11, 16 |
Index 1A08 AI TxPDO-Map Standard Ch.5
1A08:0 | AI TxPDO-Map Standard Ch.5 | PDO Mapping TxPDO 9 | UINT8 | RO | 0x09 (9dec) |
1A08:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6040:01, 1 |
1A08:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6040:02, 1 |
1A08:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6040:03, 2 |
1A08:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6040:05, 2 |
1A08:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6040:07, 1 |
1A08:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A08:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A08:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6040:0F, 1 |
1A08:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6040:10, 1 |
1A08:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6040:11, 16 |
Index 1A09 AI TxPDO-Map Compact Ch.5
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A09:0 |
AI TxPDO-Map Compact Ch.5 |
PDO Mapping TxPDO 10 |
UINT8 |
RO |
0x01 (1dec) |
1A09:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6040:11, 16 |
Index 1A0A AI TxPDO-Map Standard Ch.6
1A0A:0 | AI TxPDO-Map Standard Ch.6 | PDO Mapping TxPDO 11 | UINT8 | RO | 0x09 (9dec) |
1A0A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6050:01, 1 |
1A0A:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6050:02, 1 |
1A0A:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6050:03, 2 |
1A0A:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6050:05, 2 |
1A0A:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6050:07, 1 |
1A0A:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0A:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0A:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6050:0F, 1 |
1A0A:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6050:10, 1 |
1A0A:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6050:11, 16 |
Index 1A0B AI TxPDO-Map Compact Ch.6
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A0B:0 |
AI TxPDO-Map Compact Ch.6 |
PDO Mapping TxPDO 12 |
UINT8 |
RO |
0x01 (1dec) |
1A0B:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6050:11, 16 |
Index 1A0C AI TxPDO-Map Standard Ch.7
1A0C:0 | AI TxPDO-Map Standard Ch.7 | PDO Mapping TxPDO 13 | UINT8 | RO | 0x09 (9dec) |
1A0C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6060:01, 1 |
1A0C:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6060:02, 1 |
1A0C:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6060:03, 2 |
1A0C:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6060:05, 2 |
1A0C:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6060:07, 1 |
1A0C:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0C:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0C:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6060:0F, 1 |
1A0C:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6060:10, 1 |
1A0C:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6060:11, 16 |
Index 1A0D AI TxPDO-Map Compact Ch.7
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A0D:0 |
AI TxPDO-Map Compact Ch.7 |
PDO Mapping TxPDO 14 |
UINT8 |
RO |
0x01 (1dec) |
1A0D:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6060:11, 16 |
Index 1A0E AI TxPDO-Map Standard Ch.8
1A0E:0 | AI TxPDO-Map Standard Ch.8 | PDO Mapping TxPDO 15 | UINT8 | RO | 0x09 (9dec) |
1A0E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6070:01, 1 |
1A0E:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6070:02, 1 |
1A0E:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6070:03, 2 |
1A0E:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6070:05, 2 |
1A0E:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6070:07, 1 |
1A0E:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0E:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0E:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6070:0F, 1 |
1A0E:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6070:10, 1 |
1A0E:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6070:11, 16 |
Index 1A0F AI TxPDO-Map Compact Ch.8
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A0F:0 |
AI TxPDO-Map Compact Ch.8 |
PDO Mapping TxPDO 16 |
UINT8 |
RO |
0x01 (1dec) |
1A0F:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6070:11, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x00 (0dec) |
Index 1C13 TxPDO assign
For operation on masters other than TwinCAT it must be ensured that the channels are entered in the PDO assignment (“TxPDO assign”, object 0x1C13) successively.
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C13:0 |
TxPDO assign |
PDO Assign Inputs |
UINT8 |
RW |
0x08 (8dec) |
1C13:01 |
SubIndex 001 |
1st allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A00 (6656dec) |
1C13:02 |
SubIndex 002 |
2nd allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A02 (6658dec) |
1C13:03 |
SubIndex 003 |
3rd allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A04 (6660dec) |
1C13:04 |
SubIndex 004 |
4th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A06 (6662dec) |
1C13:05 |
SubIndex 005 |
5th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A08 (6664dec) |
1C13:06 |
SubIndex 006 |
6th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A0A (6666dec) |
1C13:07 |
SubIndex 007 |
7th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A0C (6668dec) |
1C13:08 |
SubIndex 008 |
8th allocated TxPDO (contains the index of the associated TxPDO mapping object) |
UINT16 |
RW |
0x1A0E (6670dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0000 (0dec) |
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Get cycle time | With this entry the real required process data provision time can be measured.
The entries 0x1C33:03, 0x1C33:06, 1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time *) | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
*) Designation „Delay Time“ in revision 0016
Index F009 password protection
F009:0 | Password protection | Password protection for user calibration | UINT32 | RW | 0x00000000 (0dec) |