Standard objects
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: the Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x012C1389 (19665801dec) |
Index 1008 Device name
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1008:0 |
Device name |
Device name of the EtherCAT slave |
STRING |
RO |
EL30xx |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
00 |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
01 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0xXXXX3052 |
1018:03 | Revision | Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description | UINT32 | RO | - |
1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 | UINT32 | RO | - |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardised loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1800 AI TxPDO-Par Standard Ch.1
1800:0 | AI TxPDO-Par Standard Ch.1 | PDO parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1800:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 01 1A |
Index 1801 AI TxPDO-Par Compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1801:0 |
AI TxPDO-Par Compact Ch.1 |
PDO parameter TxPDO 2 |
UINT8 |
RO |
0x06 (6dec) |
1801:06 |
Exclude TxPDOs |
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 |
OCTET-STRING[2] |
RO |
00 1A |
Index 1802 AI TxPDO-Par Standard Ch.2
1802:0 | AI TxPDO-Par Standard Ch.2 | PDO parameter TxPDO 3 | UINT8 | RO | 0x06 (6dec) |
1802:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3 | OCTET-STRING[2] | RO | 03 1A |
Index 1803 AI TxPDO-Par Compact Ch. 2
1803:0 | AI TxPDO-Par Compact Ch.2 | PDO parameter TxPDO 4 | UINT8 | RO | 0x06 (6dec) |
1803:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4 | OCTET-STRING[2] | RO | 02 1A |
Index 1804 AI TxPDO-Par Standard Ch.3
1804:0 | AI TxPDO-Par Standard Ch.3 | PDO parameter TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1804:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5 | OCTET-STRING[2] | RO | 05 1A |
Index 1805 AI TxPDO-Par Compact Ch. 3
1805:0 | AI TxPDO-Par Compact Ch.3 | PDO parameter TxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1805:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6 | OCTET-STRING[2] | RO | 04 1A |
Index 1806 AI TxPDO-Par Standard Ch.4
1806:0 | AI TxPDO-Par Standard Ch.4 | PDO parameter TxPDO 7 | UINT8 | RO | 0x06 (6dec) |
1806:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7 | OCTET-STRING[2] | RO | 07 1A |
Index 1807 AI TxPDO-Par Compact Ch. 4
1807:0 | AI TxPDO-Par Compact Ch.4 | PDO parameter TxPDO 8 | UINT8 | RO | 0x06 (6dec) |
1807:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8 | OCTET-STRING[2] | RO | 06 1A |
Index 1A00 AI TxPDO-Map Standard Ch.1
1A00:0 | AI TxPDO-Map Standard Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x0A (10dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6000:03, 2 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6000:05, 2 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6000:07, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6000:11, 16 |
Index 1A01 AI TxPDO-Map Compact Ch.1
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A01:0 |
AI TxPDO-Map Compact Ch.1 |
PDO Mapping TxPDO 2 |
UINT8 |
RO |
0x01 (1dec) |
1A01:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6000:11, 16 |
Index 1A02 AI TxPDO-Map Standard Ch.2
1A02:0 | AI TxPDO-Map Standard Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x0A (10dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6010:01, 1 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6010:02, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6010:03, 2 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6010:05, 2 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6010:07, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6010:0F, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A03 AI TxPDO-Map Compact Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A03:0 |
AI TxPDO-Map Compact Ch.2 |
PDO Mapping TxPDO 4 |
UINT8 |
RO |
0x01 (1dec) |
1A03:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6010:11, 16 |
Index 1A04 AI TxPDO-Map Standard Ch.3
1A04:0 | AI TxPDO-Map Standard Ch.3 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x09 (9dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6020:01, 1 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6020:02, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6020:03, 2 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6020:05, 2 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6020:07, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6020:0F, 1 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6020:10, 1 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6020:11, 16 |
Index 1A05 AI TxPDO-Map Compact Ch.3
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A05:0 |
AI TxPDO-Map Compact Ch.3 |
PDO Mapping TxPDO 6 |
UINT8 |
RO |
0x01 (1dec) |
1A05:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6020:11, 16 |
Index 1A06 AI TxPDO-Map Standard Ch.4
1A06:0 | AI TxPDO-Map Standard Ch.4 | PDO Mapping TxPDO 7 | UINT8 | RO | 0x0A (10dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6030:01, 1 |
1A06:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6030:02, 1 |
1A06:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6030:03, 2 |
1A06:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6030:05, 2 |
1A06:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x07 (Error) | UINT32 | RO | 0x6030:07, 1 |
1A06:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A06:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A06:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6030:0F, 1 |
1A06:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6030:10, 1 |
1A06:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6030:11, 16 |
Index 1A07 AI TxPDO-Map Compact Ch.4
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A07:0 |
AI TxPDO-Map Compact Ch.4 |
PDO Mapping TxPDO 8 |
UINT8 |
RO |
0x01 (1dec) |
1A07:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) |
UINT32 |
RO |
0x6030:11, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x00 (0dec) |
Index 1C13 TxPDO assign
For operation on masters other than TwinCAT it must be ensured that the channels are entered in the PDO assignment (“TxPDO assign”, object 0x1C13) successively.
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x04 (4dec) |
1C13:01 | SubIndex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | SubIndex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A02 (6658dec) |
1C13:03 | SubIndex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A04 (6660dec) |
1C13:04 | SubIndex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A06 (6662dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0000 (0dec) |
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Get cycle time | With this entry the real required process data provision time can be measured.
The entries 0x1C33:03, 0x1C33:06, 1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time *) | Time between SYNC1 event and reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
*) Designation „Delay Time“ in revision 0016 | |||||
Index F009 password protection
F009:0 | Password protection | Password protection for user calibration | UINT32 | RW | 0x00000000 (0dec) |
