EL3052 - Connection, display and diagnostics
EL3052 Connection
Terminal point | Description | Internally connected | Max. current carrying capacity *) | |
Name | No. | |||
Input 1 | 1 | Input 1 | - | 40 mA |
24 V | 2 | 24 V | 6; positive power contact | 1 A |
0 V | 3 | 0 V | 7; negative power contact | 1 A |
Shield | 4 | Shield (FE) | 8; DIN rail | 100 mA **) |
Input 2 | 5 | Input 2 | - | 40 mA |
24 V | 6 | 24 V | 2; positive power contact | 1 A |
0 V | 7 | 0 V | 3; negative power contact | 1 A |
Shield | 8 | Shield (FE) | 4; DIN rail | 100 mA **) |
*) Constant and peak value | ||||
![]() | Overcurrent protection of the 20 mA inputs The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
EL3052 - LEDs
LED | Color | Meaning | |
RUN *) | green | These LEDs indicate the terminal's operating state: | |
off | State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal | ||
flashing | State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set | ||
single flash | State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks. | ||
on | State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible | ||
ERROR **) | red | Fault indication for broken wire and if the measuring range for the respective channel is exceeded (under- or overrun) | |
*) If several RUN LEDs are present, all of them have the same function. | |||
