EL3048 - Connection, display and diagnostics
EL3048 - Connection, display and diagnostics 1:Fig.40: Connection EL3048
EL3048 - Connection
Terminal point
Internally connected
with connection
Max. current carrying capacity *)
No.
Input 1
1
Input 1
40 mA
Input 3
2
Input 3
40 mA
Input 5
3
Input 5
40 mA
Input 7
4
Input 7
40 mA
Input 2
5
Input 2
40 mA
Input 4
6
Input 4
40 mA
Input 6
7
Input 6
40 mA
Input 8
8
Input 8
40 mA
*) Constant and peak value
EL3048 - Connection, display and diagnostics 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
  • In the event of a fault, the current limiter must not be overloaded by a voltage > 30 V from the source device.
  • Overcurrent is displayed in the process image as "Overrange".
  • After occurrence, the error condition must be stopped immediately, the source device switched off or disconnected from the input terminal.
  • If the error condition persists for a longer period of time, the internal terminal current limitation reduces the absorbed signal current for thermal reasons, depending on the ambient conditions also below 20 mA.
EL3048 - LEDs
EL3048 - Connection, display and diagnostics 3:Fig.42: EL3048 - LEDs
LED
Color
Meaning
ERROR **)
red
Fault indication for broken wire and if the measuring range for the respective channel is exceeded
**) The error display shows the signal processing state for each channel