EL3044 - Connection, display and diagnostics
EL3044 - Connection, display and diagnostics 1:Fig.37: EL3044 – Connection
EL3044 - Connection
Terminal point
Internally connected
with connection
Max. current carrying capacity *)
No.
Input 1
1
Input 1
40 mA
GND
2
Signal ground for input 1
4, 6, 8
40 mA
Input 3
3
Input 3
40 mA
GND
4
Signal ground for input 3
2, 6, 8
40 mA
Input 2
5
Input 2
40 mA
GND
6
Signal ground for input 2
2, 4, 8
40 mA
Input 4
7
Input 4
40 mA
GND
8
Signal ground for input 4
2, 4, 6
40 mA
*) Constant and peak value
EL3044 - Connection, display and diagnostics 2:
Overcurrent protection of the 20 mA inputs
The current inputs are protected against damage by overcurrent by an internal current limitation, currents > 30 mA may occur.
  • In the event of a fault, the current limiter must not be overloaded by a voltage > 30 V from the source device.
  • Overcurrent is displayed in the process image as "Overrange".
  • After occurrence, the error condition must be stopped immediately, the source device switched off or disconnected from the input terminal.
  • If the error condition persists for a longer period of time, the internal terminal current limitation reduces the absorbed signal current for thermal reasons, depending on the ambient conditions also below 20 mA.
EL3044 - LEDs
EL3044 - Connection, display and diagnostics 3:Fig.21: EL3044 - RUN and ERROR LED
LED
Color
Meaning
RUN *)
green
These LEDs indicate the terminal's operating state:
off
State of the EtherCAT State Machine: INIT = initialization of the terminal or BOOTSTRAP = function for firmware updates of the terminal
flashing
State of the EtherCAT State Machine: PREOP = function for mailbox communication and different standard-settings set
single flash
State of the EtherCAT State Machine: SAFEOP = verification of the Sync Manager channels and the distributed clocks.
Outputs remain in safe state
on
State of the EtherCAT State Machine: OP = normal operating state; mailbox and process data communication is possible
ERROR **)
red
Fault indication for broken wire and if the measuring range for the respective channel is exceeded (under- or overrun)
*) If several RUN LEDs are present, all of them have the same function.
**) The error display shows the signal processing state for each channel.