EL3014 - Technical data
Technical data
EL3014
analog inputs
4
Signal current
0…20 mA
Internal resistance
85 Ω typ. + diode voltage
Input filter cut-off frequency
1 kHz
Common-mode voltage Ucm
max. 10 V
Conversion time
(default setting: 50 Hz filter)
typ. 0.625 ms default, configurable
Resolution
12 bits (16 bits presentation, including sign)
Sampling type
multiplex
Ground reference
differential
Support NoCoeStorage
yes
Measuring error
relative to the full scale value (full measuring range)
< ±0.5% below 0°C
< ±0.3% at 0°C ... +55°C
< ±0.5% above 55°C
(observe permissible ambient temperature range!)
Power supply for the electronics
via the E-bus
Current consumption via E‑bus
typ. 130 mA
Electrical isolation
500 V (E-bus/field voltage)
Bit width in process image (default setting)
2 bytes status, 2 bytes value per channel
Configuration
no address or configuration settings required
Weight
approx. 55 g
Permissible ambient temperature range during operation
-25°C ... +60°C
Permissible ambient temperature range during storage
-40°C ... +85°C
Permissible relative air humidity
95%, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm)
Installation
on 35 mm mounting rail, conforms to EN 60715
Enhanced mechanical load capacity
yes, see also Installation instructions for enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Approvals / markings*)
CE, EAC, UKCA, CCC
ATEX, IECEx, cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex ec IIC T4 Gc
IECEx
Ex ec IIC T4 Gc