General information on commissioning the EL3008-0003, EL3008-0005
The EL3008-000x has 8 analog inputs. By default setting, the terminal operates with the 8 x analog input configuration using Real32 PDOs.
The input channels are set to Interface ±3 V (EL3008-0003) or ±5°V (EL3008-0005), floating point, extended range.

The terminal contains several functions that are controlled by
- enabling/disabling cyclic process data (PDO) at commissioning time in the EtherCAT master,
- setting/changing so-called CoE settings in the device; this can be done at runtime.
The functions of this terminal are explained in the following commissioning chapter “Functional units of the analog inputs”.
for CoE parameterization:
- CoE registers are listed below; the “n” in the index represents the channel number in the terminal:
Channel 1: n = 0, Channel 2: n = 1, … - The CoE values cannot be read in real time; they are updated in the TwinCAT online display approximately once per second. The controller can also read them via ADS (and, depending on their type, write them), with update rates as short as a few ms, depending on the EtherCAT cycle time.
- Before initial commissioning, it may be useful to reset the CoE parameters of the terminal using CoE reset by entering the value to 0x1011:01; this covers all channels
(see the EtherCAT system manual, chapter“Restoring delivery state”) - “Default” or “default setting” refers to the factory setting or the setting restored by a CoE reset.

Temporal operating behavior of the EL3008-000x
The terminal operates constantly with the conversion time specified in the “Filter” chapter, regardless of the EtherCAT cycle time applied. It supports the following EtherCAT operation modes:
- “FreeRun”: yes
if the filter is enabled:
Regardless of the EtherCAT cycle, the terminal processes its AI/AO data at the conversion rate specified in the “Filter” chapter.
EtherCAT cycle times supported by the terminal: 100 µs…100 ms - “SM-Synchron” (frame-triggered): no
- Distributed Clocks: no