Technical data
Analog input | EL3008-0003 | EL3008-0005 | |||
Analog inputs | 8 | ||||
Function | Voltage measurement | ||||
Wiring | 2-wire | ||||
Ground reference | Cascaded channels | ||||
Max. sampling rate | min. 2 ms (max. 500 sps) per channel 1) | ||||
Sampling type | Multiplex Ch. 1…8, each approx. 125 µs delay between Ch n/n+1 | ||||
Internal resistance to AGND | > 8 MΩ | Connections 1 and 9: ~200 kΩ | |||
Input filter cut-off frequency | 1.5 kHz (-3 dB, 1st-order low-pass filter) | ||||
Settling time | Filter IIR8 (default): 1 s typ. (0%…90%) Filter disabled: 2 ms typ. (0%…90%) | ||||
Dielectric strength | max. ±25 V per channel against AGND (temporary and permanent) | max. ±50 V per channel against AGND (temporary and permanent) | |||
Measuring range, nominal (FSVnom) | -3 V…+3 V | -5 V…+5 V | |||
Measuring range, technical (FSVtechn) | -3.22 V…+3.22 V | -5.35 V…+5.35 V | |||
Resolution | 16 bits (including sign) | ||||
Conversion method | SAR | ||||
Measuring error/uncertainty | < ±0.1%FSV typ. at 25°C ±5°C (observe permissible ambient temperature range!) | < ±0.1%FSV typ. at 25°C ±5°C (observe permissible ambient temperature range!) | |||
Temperature coefficient TkGain | 35 ppmFSV/K typ. 1) | ||||
Temperature coefficient TkOffset | Tbd. | ||||
Noise | ±0.2 mV / 66 ppmFSV (with IIR8 filter) 1) | ||||
Channel crosstalk | typ. < -70 dB 1) | ||||
Largest short-term deviation during a specified electrical interference test | ±1%FSV typ. | ||||
Electrical isolation channel/channel | no | ||||
1) Preliminary information | |||||
General | EL3008-0003 | EL3008-0005 |
Power supply | via the E-bus | |
Distributed clocks | – | |
Electrical isolation channel/E-bus | Reinforced insulation in accordance with EN 61010-2-030, EN 60664-1 Production test 6 kV DC Type Test: 6.4 kV DC / 1 min; 7.4 kV DC / 5 s | |
Electrical isolation channel/SGND | - (SGND not available) | |
Measurement category / overvoltage category | 300 V CAT II; with contact protection cover 1500 V CAT II; according to EN 61010-2-030 Notes:
Current consumption via E-bus | 190 mA typ. | |
Current consumption via power contacts | not present | |
Min. EtherCAT cycle time | 100 µs | |
Special properties | Cascaded channels, extended range 107%, FIR/IIR filter can be enabled | |
EMC immunity/emission | conforms to EN 61000-6-2/EN 61000-6-4 | |
Configuration | Via the EtherCAT master, e.g., TwinCAT | |
Approvals/markings*) | CE, | |
Mechanical properties | EL3008-0003 | EL3008-0005 |
Connection type | 10-pin Push-in connector plug, service plug (25 mating cycles) Solid/stranded wire 0.14…1.5 mm², stripping length 8 mm with ferrule 0.28…1.0 mm² No pulling/plugging under voltage permitted | |
Weight | approx. 90 g | |
on 35 mm DIN mounting rail, conforms to EN 60715 | ||
Operating temperature | -25…+60°C | 0…55°C |
Storage temperature | -40…+85°C | -25…+85°C |
Relative humidity | 95%, no condensation | |
Protection rating | IP20 | |
Installation position | variable | |
Vibration/shock resistance | conforms to EN 60068-2-6/EN 60068-2-27 | |
Installation note | 10-pin plug included in the scope of delivery Contact protection cover ZS9100-0005 included in the scope of delivery | |
Permissible operating altitude range | 0…2000 m (according to EN 61010-1) | |
Pollution degree | 2 or better (according to EN 61010-1) | |