Technical data
Technical data | EL1804 | EL1814 |
Connection technology | 3-wire | |
Number of inputs | 4 | |
Nominal voltage of inputs | 24 VDC (-15% / +20%) | |
Signal voltage "0" | -3 V ... 5 V (EN 61131-2, type 1/3) | |
Signal voltage "1" | 11 V ... 30 V (EN 61131-2, type 1/3) | |
Input filter | 3 ms | 10 µs |
Input current | typically 3 mA (EN 61131-2, type 3) | |
Supply voltage for electronic | via power contacts | |
Current consumption power contacts | typ. 2 mA + load | |
Current consumption via E-bus | typ. 90 mA | |
Electrical isolation | 500 V (E-bus/field voltage) | |
Bit width in process image | 4 input bits | |
Configuration | no address or configuration settings required | |
Conductor types | solid wire, stranded wire and ferrule | |
Conductor connection | solid wire conductors: direct plug-in technique; stranded wire conductors and ferrules: spring actuation by screwdriver | |
Rated cross-section | solid wire: 0.08…1.5 mm²; stranded wire: 0.25...1.5 mm²; ferrule: 0.14…0.75 mm² | |
Weight | approx. 60 g | |
Permissible ambient temperature range during operation | -25 °C ... +60 °C | |
Storage temperature | -40 °C ... +85 °C | |
Relative humidity | 95%, no condensation | |
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (connected width: 12 mm) | |
on 35 mm mounting rail according to EN 60715 | ||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC resistance burst/ESD | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Protection class | IP20 | |
Installation position | variable | |
Marking / Approval*) | ||
Ex markings
Standard | Marking |
ATEX | II 3 G Ex ec IIC T4 Gc |
IECEx | Ex ec IIC T4 Gc |