Configuration data
Index 8pp0 MTI settings (for 00 ≤ pp ≤ 07; Ch. 1 to Ch. 8)
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default | |
8pp0:0 |
MTI settings |
UINT8 |
RO |
0x14 (20dec) | |
8pp0:01 |
Enable digital filter |
Activation of the filter to hide spikes. The filter length should be entered in 8pp0:14 "DigitalFilterCount" (further explanation see here). |
BOOLEAN |
RW |
0x00 (0dec) | |
8pp0:11 |
Buffer reset behavior |
Specifies the behavior of the "Input buffer reset" bit Permitted values: |
UINT16 |
RW |
0x0000 (0dec) | |
0 |
Reset on rising edge: The buffer is cleared with a rising edge of "Input buffer reset" | |||||
1 |
Reset on high level: The buffer is cleared with a rising edge of "Input buffer reset" and does not accept new values until "Input buffer reset" is reset. | |||||
8pp0:12 |
Buffer mode |
Specifies whether handshaking is to be used for retrieving the values from the buffer (transmission integrity) or whether new values are to be transferred directly with each PLC cycle (faster). Permitted values (further explanation see here): |
UINT16 |
RW |
0x0001 (1dec) | |
0 |
Asynchronous (Buffered): The arrival of new events must be acknowledged by the PLC. To this end the byte "No of input events" must be monitored in the PLC program. If it is greater than zero the pending events can be taken over from the process image. Subsequently the byte "Input order counter" must be incremented. This signals the terminal that the events were accepted and new data can be created in the next cycle. | |||||
1 |
Synchronous: New events are automatically transferred with each PLC cycle | |||||
8pp0:13 |
Buffer overflow behavior |
Specifies the behavior in the event of buffer overflow Permitted values: |
UINT16 |
RW |
0x0000 (0dec) | |
0 |
Lock buffer: New events are discarded | |||||
1 |
Overwrite oldest event: New events overwrite the last events in the buffer | |||||
8pp0:14 |
Digital filter count |
Defines the number of event samples to ensure transfer into the buffer (further explanation see here). |
UINT16 |
RW |
0x0001 (1dec) | |
Index 8ppF MTI Vendor data (for 00 ≤ pp ≤ 07; Ch. 1 to Ch. 8)
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
8ppF:0 |
MTI Vendor data |
UINT8 |
RO |
0x12 (18dec) |
8ppF:11 |
Offset pos |
This object can be used to move the input time of the rising edges. This setting is left to the manufacturer. |
INT32 |
RW |
0x00000000 (0dec) |
8ppF:12 |
Offset neg |
This object can be used to move the input time of the falling edges. This setting is left to the manufacturer. |
INT32 |
RW |
0x00000000 (0dec) |
Index 8pp0 TSI Settings (for 08 ≤ pp ≤ 0F; Ch. 1 to Ch. 8)
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default | |
8pp0:0 |
TSI Settings |
UINT8 |
RO |
0x02 (2dec) | |
8pp0:01 |
Pos Sample Mode |
During each PLC cycle only one rising edge may be detected at the terminal input. If several edges arrive during a cycle, this bit can be used to decide which edge should be shown in the process image. Permitted values: |
BIT1 |
RW |
0x00 (0dec) | |
0 |
Last edge: The last edge of the preceding PLC cycle is shown | |||||
1 |
First edge: The first edge of the preceding PLC cycle is shown | |||||
8pp0:02 |
Neg Sample Mode |
During each PLC cycle only one falling edge may be detected at the terminal input. If several edges arrive during a cycle, this bit can be used to decide which edge should be shown in the process image. Permitted values: |
BIT1 |
RW |
0x00 (0dec) | |
0 |
1 |
Index 8ppF TSI Vendor data (for 08 ≤ pp ≤ 0F; Ch. 1 to Ch. 8)
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
8ppF:0 |
TSI Vendor data |
UINT8 |
RO |
0x12 (18dec) |
8ppF:11 |
Offset pos |
INT32 |
RW |
0x00000000 (0dec) |
8ppF:12 |
Offset neg |
INT32 |
RW |
0x00000000 (0dec) |
