EK9300 EtherCAT configuration
The EK9300 is an EtherCAT master with automatic configuration, i.e. all EtherCAT terminals must always be present when switching on the system. Since the boot-up of the EK9300 generally takes considerably longer than the start-up of the EtherCAT slave devices, the latter can be operated on the same power supply. With decentralized EtherCAT slaves, care must be taken that they are switched on earlier or at the same time as the supply voltage.
Switching EtherCAT devices on or off during the runtime
If one or more EtherCAT devices should fail during the operating phase, a plug alarm is sent; the EK9300 remains in data exchange. The input data of all EtherCAT devices are invalid and are set to FALSE or ZERO; the output data are no longer accepted. This also applies to the devices that are still in operation on the EK9300. If you wish to use the option to plug in or unplug devices during the runtime, a further “Sync Unit” must be configured. This is not possible with an EK9300. In this case use a CX8093.
EtherCAT devices that don’t exist in the GSDML
Some EtherCAT Slaves are not included in the GSDML and thus cannot be used (yet). The CX8093 can be used here, since it supports all EtherCAT devices in principle.
EtherCAT topology
All EtherCAT devices must be entered in the order in which they map themselves on the EK9300 and thus on the EtherCAT master. EtherCAT devices are addressed automatically; with a few exceptions all EtherCAT Bus Terminals are equipped with an EtherCAT ASIC, which has to be entered in the system, i.e. the PROFINET controller. EtherCAT Terminals without an ASIC are, for example, EL9400, EL9070 and other EL9xxx. You can identify these EtherCAT Terminals using the technical data "Message to E-bus". If there is a “-” here, this terminal does not have to be entered in the PROFINET controller.
EtherCAT devices are registered in the direction of the EtherCAT telegram.
Sample configuration with EK1100 EtherCAT coupler
EK9300 EtherCAT configuration 1:Fig.22: Sample configuration with EK1100 EtherCAT coupler
Sample configuration with EPxxxx EtherCAT Box
EK9300 EtherCAT configuration 2:Fig.23: Sample configuration with EPxxxx EtherCAT Box
Sample configuration with EK1122 2-port EtherCAT junction
The counting direction is to be observed when using an EK1122. If EtherCAT junction 1 on the EK1122 is connected, then the EtherCAT frame is forwarded here first (1); if junction 1 is not connected the frame on junction 2 is sent (2), only after that does the sequence continue with the E-bus on the right-hand side (3).
EK9300 EtherCAT configuration 3:Fig.24: Sample configuration with EK1122 2-port EtherCAT junction
If both junctions are not used, then junction 1 and 2 are short-circuited as it were and the EC frame continues directly from the terminal to the right.
It must be noted that in the PROFINET controller the modules are entered in the direction of the EtherCAT frame.
Sample configuration with EP1122 2-port EtherCAT junction
The counting direction is to be observed when using an EP1122; it is comparable with the EK1122. If EtherCAT junction 1 on the EP1122 is connected, then the EtherCAT frame is forwarded here first (1); if junction 1 is not connected the frame on junction 2 is sent (2), only after that does the sequence continue with the EC-bus on the right-hand side (3).
EK9300 EtherCAT configuration 4:Fig.25: Sample configuration with EP1122 2-port EtherCAT junction
EK9300 EtherCAT configuration 5:
Connection during operation
You cannot use the EP1122 and EK1122 for Hot Swap or connect or disconnect them during operation. The EP1122 and EK1122 are suitable in conjunction with the EK coupler only as topology extensions (star).
