Commissioning EL72x1-xxxx
The EK9300 supports the servo terminals with the "Drive Motion Control" mode. This mode enables an axis to move independently to a position assigned from the process data. The setpoint calculations, which are usually done by the NC, are done in DMC mode by the terminal itself.
The commissioning of an EL7201-0010 on the EK9300 is to be shown by means of an example.
Requirement:
Hardware used
Configuration
First, the EK9300 and the EL7201-0010 must be added to the configuration. See: Appending PROFINET devices
To ensure that the terminal uses the correct motor, it is recommended to read the motor name plate with the terminal. For this the parameter entries "Enable auto config", "Reconfig identical motor" and "Reconfig non-identical motor" in the parameter settings "FB OCT SettingsCh1 - Index 0x3008" of the terminal must be changed to "TRUE".
Commissioning EL72x1-xxxx 1:Fig.29: Parameter settings for automatic readout of the motor name plate used
The terminal reads the name plate of the motor and sets the motor-specific parameters automatically. The default motor settings are not used any further and can be read back if required.
Mapping of the EL7201-0010 in "Drive Motion Control" format
INPUTS (64 bytes):
Commissioning EL72x1-xxxx 2:Fig.30: Drive Motion Control Inputs
Size (variable)
Bit offset
DMC Inputs.FeedbackStatus (16-bit array)
Latch extern valid
BIT (BOOL)
0.1
Set counter done
BIT (BOOL)
0.2
Status of extern latch
BIT (BOOL)
1.4
DMC Inputs.DriveStatus (16-bit array)
Ready to enable
BIT (BOOL)
2.0
Ready
BIT (BOOL)
2.1
Warning
BIT (BOOL)
2.2
Error
BIT (BOOL)
2.3
Moving positive
BIT (BOOL)
2.4
Moving negative
BIT (BOOL)
2.5
Digital input 1
BIT (BOOL)
3.3
Digital input 2
BIT (BOOL)
3.4
DMC Inputs.PositioningStatus (16-bit array)
Busy
BIT (BOOL)
4.0
In-Target
BIT (BOOL)
4.1
Warning
BIT (BOOL)
4.2
Error
BIT (BOOL)
4.3
Calibrated
BIT (BOOL)
4.4
Accelerate
BIT (BOOL)
4.5
Decelerate
BIT (BOOL)
4.6
Ready to execute
BIT (BOOL)
4.7
DMC Inputs.Set position
DWORD (32-bit)
6-9
DMC Inputs.aligned [0]
DWORD (32-bit)
10-13
DMC Inputs.Set velocity
WORD (16-bit)
14-15
DMC Inputs.Actual drive time
DWORD (32-bit)
16-19
DMC Inputs.Actual position lag
DWORD (32-bit)
20-23
DMC Inputs aligned [1]
DWORD (32-bit)
24-27
DMC Inputs.Actual velocity
WORD (16-bit)
28-29
DWORD (32-bit)
30-33
DMC Inputs.aligned [2]
DWORD (32-bit)
34-37
DMC Inputs.Error Id
DWORD (32-bit)
28-41
DMC Inputs.Input cycle counter
Byte (8 bit)
42
DMC Inputs.aligned [3]
Byte (8 bit)
43
DMC Inputs.Latch value input
DWORD (32-bit)
44-47
DMC Inputs.aligned [4]
DWORD (32-bit)
48-51
DMC Inputs. Cycle info data1
WORD (16-bit)
52-53
DMC Inputs.Cycle info data2
WORD (16-bit)
54-55
DMC Inputs.aligned [5]
LWORD (64-bit)
56-63
OUTPUTS (40 bytes):
Commissioning EL72x1-xxxx 3:Fig.31: Drive Motion Control Outputs
Size (variable)
Bit offset
DMC Outputs.FeedbackControl (16-bit array)
Latch extern valid
BIT (BOOL)
0.1
Set counter done
BIT (BOOL)
0.2
BIT (BOOL)
1.4
DMC Outputs.DriveControl (16-bit array)
Enable
Bit (BOOL)
2.0
Reset
Bit (BOOL)
2.1
DMC Outputs.PositioningControl (16-bit array)
Execute
BIT (BOOL)
4.0
Emergency Stop
BIT (BOOL)
4.1
DMC Outputs.Set counter value
DWORD (32-bit)
6-9
DMC Outputs.aligned [0]
DWORD (32-bit)
10-13
DMC Outputs.Target position
DWORD (32-bit)
14-17
DWORD (32-bit)
18-21
DMC Outputs.Target velocity
WORD (16-bit)
22-23
DMC Outputs.Start Type
WORD (16-bit)
24-25
DMC Outputs.Target acceleration
WORD (16-bit)
26-27
DMC Outputs.Target deceleration
WORD (16-bit)
28-29
10 bytes
30-39
Program sequence
1) The position of one revolution is 0x0010_0000 220
2)
The velocity is given in 0.01 % of the maximum velocity; 1000 = 10 %
3) The acceleration ramp is given in ms; 1000(dec) = 1 sec
4) see table
ABSOLUTE
0x0001
Absolute positioning to a specific target position
RELATIVE
0x0002
Relative positioning to a calculated target position; a specified position difference is added to the current position
ENDLESS_PLUS
0x0003
Endless travel in the positive direction of rotation (direct specification of a velocity)
ENDLESS_MINUS
0x0004
Endless travel in the negative direction of rotation (direct specification of a velocity)
MODULO_SHORT
0x0105
Modulo positioning along the shortest path to the modulo position (positive or negative), calculated by the "modulo factor"
MODULO_PLUS
0x0205
Modulo positioning in the positive direction of rotation to the calculated modulo position
MODULO_MINUS
0x0305
Modulo positioning in the negative direction of rotation to the calculated modulo position
CALI_PLC-CAM
0x6000
Start a calibration with cam (digital inputs)
CALI_ON_BLOCK
0x6200
Start a calibration "on block".
CALI_SET_POS
0x6E00
Set as calibrated, do not change position
CALI_CLEAR_POS
0x6F00
Delete calibration bit
Commissioning EL72x1-xxxx 4:
Creating a task for commissioning via TwinCAT
For commissioning via TwinCAT with our PROFINET controllers, a separate task must be created for the outputs, otherwise the values will not be processed correctly.
Servo terminal with STO input:
If the terminal in use is to have an STO input, this can lead to an error if it is not supplied with power.
A distinction must be made here between two cases, i.e. which error occurs.
Commissioning EL72x1-xxxx 5:Fig.32: Display of the Error ID if the STO input is absent
It is possible to show the state of the STO input in the process data. For this purpose, the option "Input level" must be selected in the parameter settings of the terminal under "DRV Amplifier Settings Ch. 2 - Select Info data x". The state is then displayed in the eighth bit of the "Cyclic info data x".
Commissioning EL72x1-xxxx 6:
Parameter settings for showing the STO input in the process data
Using the EL7201-0010 via the TIA portal