Note the structure of the DPV1 telegram
Index | 100 |
Slot number | Position of the EtherCAT Terminal, absolute position plus 1 |
Structure | Meaning | Length in bytes |
CoE Index | CoE index number. | 2 |
COE subindex | COE subindex number. | 1 |
READ/ WRITE | 0-read/ 1-write. | 1 |
Length | Length of the data that is to be written. During reading, this can be zero. | 4 |
Data | Data, only required for writing. | n |
If you use virtual slaves, the slot number must contain the actual terminal position, not the slot position of the EtherCAT Terminal.
Example
You want to read the COE data of EtherCAT Terminal EL3154. This EtherCAT Terminal is configured in TwinCAT under slave 2 (virtual slave).
Slave 1 | Slave 2 (virtual slave) | ||||||||||
EK3100 | CtrlStatus | EL1008 | EL2008 | EL3062 | EK1110 | EK3100 | CtrlStatus | EK1100 | EL2008 | EL1008 | EL3154 |
PROFIBUS address: 11 | PROFIBUS address: 12. The non-visible EL9011 is omitted. | ||||||||||
In this example EtherCAT Terminal EL3154 has the slot number 9. The CtrlStatus DWORD module is not included in the count for the EK3100 virtual slave.
Slot number | 2 | 3 | 4 | 5 | 6 | 7 | 8 | 9 |
EK3100 | EL1008 | EL2008 | EL3062 | EK1110 | EK1100 | EL2008 | EL1008 | EL3154 |
![]() | Reading CoE data To read CoE data, the data to be read must first be written with a DPV1-Write, and only then can the data be read with a DPV1-READ. |