Connection EK1322
Connection EK1322 1:
EK1322 feed-in connections
Terminal point
No.
US 24 V
1
+24 V Feed-In US (System- and Sensor supply)
US 0 V
2
0 V of System- and Sensor supply US
UP 24 V
3
+24 V Feed-In UP (Peripheral voltage for Actors)
UP 0 V
4
0 V of Peripheral voltage for Actors UP
Permitted conductor cross-sections of the terminal points for input US/UP
The permitted conductor cross-sections and the strip length are shown in the following table.
Terminal points, clamping range
0.13 ... 1.5 mm2
Wire cross-section (AWG)
28 – 14
Solid wire H05(07) V-U
0.2 ... 1.5 mm2
Stranded wire H05(07) V-K
0.2 ... 1.5 mm2
Stranded wire (with ferrule with collar DIN46 228/4)
0.25 ... 0.75 mm2
Stranded wire (with ferrule DIN 46 228/1)
0.25 ... 1.5 mm2
Strip length
approx. 8 ... 9 mm