Technical data
Technical data
EK1101-0010
Task in the EtherCAT system
Coupling of EtherCAT Terminals (ELxxxx) to 100BASE-TX or BroadR EtherCAT P networks
Extended distance connection
Number of EtherCAT Terminals
up to 65535 in the overall system
Number of peripheral signals
max. 4.2 GB addressable I/O points
Data transfer medium
Ethernet 100BASE - TX (at least Ethernet CAT5 cable)
Cable length between 2 bus couplers
max. 100 m (100BASE-TX)
max. 300 m (copper, Cat. 5, 4-wire) for connection between two couplers with extended distance connection
max. 200 m (copper, Cat. 5, 4-wire) for connection between two couplers with extended distance connection,
at ambient temperature < 0°C or > +55°C
Protocol / Baud rate
EtherCAT Device Protocol / 100 MBaud
HotConnect
max. number of configurable IDs: 4096
Propagation delay
1 µs typ.
Bus connection
2 x RJ45
Power supply
24 VDC (-15 %/+20 %)
Current consumption
90 mA + (∑ E-bus current)/4
E-bus power supply (5 V)
dependent on the ambient temperature
(at higher current consumption the EL9410 power supply terminal can be used in addition)
max. 2 A (-25°C ... +55°C)
max. 1 A (> +55°C)
Power contacts
max. 24 VDC, max. 10 A
Electrical isolation
500 V (power contact/supply voltage/EtherCAT)
Dimensions (W x H x D)
approx. 44 mm x 100 mm x 68 mm
Weight
approx. 105 g
Permissible ambient temperature range during operation
-25 °C ... +60 °C
Permissible ambient temperature range during storage
-40 °C... + 85 °C
Permissible relative air humidity
95 %, no condensation
Installation
on 35 mm mounting rail, conforms to EN 60715
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP20
Installation position
variable
Approvals / markings*)
CE, EAC, UKCA,
cULus