Technical data
Technical data | EK1101-0010 |
Task in the EtherCAT system | Coupling of EtherCAT Terminals (ELxxxx) to 100BASE-TX or BroadR EtherCAT P networks |
Number of EtherCAT Terminals | up to 65535 in the overall system |
Number of peripheral signals | max. 4.2 GB addressable I/O points |
Data transfer medium | Ethernet 100BASE - TX (at least Ethernet CAT5 cable) |
Cable length between 2 bus couplers | max. 100 m (100BASE-TX) |
max. 300 m (copper, Cat. 5, 4-wire) for connection between two couplers with extended distance connection | |
max. 200 m (copper, Cat. 5, 4-wire) for connection between two couplers with extended distance connection, | |
Protocol / Baud rate | EtherCAT Device Protocol / 100 MBaud |
HotConnect | max. number of configurable IDs: 4096 |
Propagation delay | 1 µs typ. |
Bus connection | 2 x RJ45 |
Power supply | 24 VDC (-15 %/+20 %) |
Current consumption | 90 mA + (∑ E-bus current)/4 |
E-bus power supply (5 V) (at higher current consumption the EL9410 power supply terminal can be used in addition) | max. 2 A (-25°C ... +55°C) |
max. 1 A (> +55°C) | |
Power contacts | max. 24 VDC, max. 10 A |
Electrical isolation | 500 V (power contact/supply voltage/EtherCAT) |
Dimensions (W x H x D) | approx. 44 mm x 100 mm x 68 mm |
Weight | approx. 105 g |
Permissible ambient temperature range during operation | -25 °C ... +60 °C |
Permissible ambient temperature range during storage | -40 °C... + 85 °C |
Permissible relative air humidity | 95 %, no condensation |
on 35 mm mounting rail, conforms to EN 60715 | |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection rating | IP20 |
Approvals / markings*) | CE, EAC, UKCA, |