Principles of fiber-optic technology
When using fiber-optic cables for the transmission of data, there are various factors that influence the signal transmission and have to be observed in order to guarantee reliable transmission. Important principles of fiber-optic technology are described below.
Attenuation
Less light reaches the end of a connection with fiber-optic cables than is input at the start of the connection. This loss of light between the start and end of the transmission link is called attenuation. The attenuation between two points is often stated in decibels (dB). However, the decibel is not a unit, but a ratio – in the case of a fiber-optic cable it is the ratio of the light energy at the start of the connection to that at the end. It is one tenth of a Bel (B) (1 B = 10 dB). In general, decibel indicates a power level LP from the ratio of one power P1 to another power P2.
- LP[dB] = 10*log10(P1/P2)
A positive power factor is a signal amplification, a negative power factor conversely a weakening or attenuation of the signal.
The attenuation of a fiber-optic connection is essentially determined by three influencing factors. These influencing factors are the attenuation in the fiber-optic, the attenuation in the connector and the attenuations that result from the splices in the fiber-optic connection. The total attenuation is therefore given by
- Fiber-optic link attenuation [dB] = fiber loss attenuation [dB] + connector insertion attenuation [dB] + splice insertion attenuation [dB]
Where
- fiber loss attenuation [dB] = fiber attenuation coefficient [dB/km)] x length [km]
- connector insertion attenuation [dB] = number of connectors x connector insertion attenuation [dB]
- splice insertion attenuation [dB] = number of splices x splice insertion attenuation [dB]
Dispersion
A further influence that needs to be observed with the signal transmission is the dispersion. Dispersion describes the spreading or widening of a light pulse. Due to propagation differences resulting in the fiber-optic cable from different injection angles of the light waves, the optical pulse widens and is therefore wider at the output than at the input. The longer the transmission link, the greater the dispersion.
Fig.49: DispersionIf higher data rates are to be transmitted by the fiber-optic cable, the pulses must be sent faster at the input. What may happen then, however, is that pulses at the output run into one another and can no longer be distinguished from one another. The dispersion thus limits the maximum bandwidth of the fiber-optic connection.
The maximum bandwidth is specified in the data sheet for a fiber-optic cable as the bandwidth/length ratio in the unit MHz*km. Therefore, the longer a transmission link, the smaller the available bandwidth. The bandwidth/length ratio or product is always specified in the data sheet for a fiber-optic cable. The length of the transmission link can then be calculated with the necessary bandwidth.
s [km] = bandwidth [MHz] / bandwidth/length ratio [MHz/km]
Further influences on the signal transmission
In addition to the main influences (attenuation and dispersion) that limit the transmission link, care must be taken when installing and maintaining fiber-optic transmission links.
Sharp kinks and micro-bends in the fiber-optic lead to additional reflections in the fiber, as a result of which the influences of the attenuation and dispersion are increased. The specified bending radii of fiber-optic cables must be adhered to.
Poorly installed connectors also have a great influence on the signal quality. In case of poor connections, the fiber-optic may be too far away from the connecting piece, so that the light waves do not enter the fiber at the right angle of entry.
The third influence on the signal transmission that needs to be observed is soiling of, or damage to the ends of optical fibers. Due to the size of the fibers, often just 125 µm, dirt or damage cannot be discerned with the naked eye. Only a microscope with a sufficient magnification (at least factor 100) enables the fiber ends to be checked. To prevent soiling, the cable cap supplied with the cable should always be fitted to the fiber end.
Power and attenuation budget
The power budget specifies the minimum power available between transmitter and receiver. The attenuation budget describes the attenuation between transmitter and receiver due to the three attenuation factors – fiber, connectors and splices – described above.
Transceivers (derived from the words transmitter and receiver) are installed in fiber-optic transmitters and receivers. A transceiver is a combined transmitting and receiving device. The transceiver data sheet usually contains two key values that are required for calculating the power budget. These values are the minimum output power (worst level) of the transmitter and the maximum sensitivity (i.e. lowest received power/level) of the receiver at which it still recognizes signals.
Both values are often specified in the unit decibel milliwatt (dBm). dBm describes the power level in relation to a reference value of 1 mW.
LP[dB] = 10*log10(P1/1 mW)0 dBm then corresponds to a power value of 1 mW, positive dBm values indicate power values >1 mW and negative dBm values indicate power values <1 mW.
For the technical application assessment, the difference between the minimum output power and the maximum sensitivity at the input is therefore regarded as the available power budget as a worst-case assumption:
Leistungsbudget = minimale Ausgangsleistung - maximale EmpfindlichkeitNote: In practice, the power budget is usually higher because the typical transmission power is higher than the minimum. However, this is not always the case.
Cable attenuation results from the attenuation influences described above.
Dämpfungspegel [dB] = Faserverlustdämpfung [dB] + Steckereinfügungsdämpfung [dB] + Spleißeinfügungsdämpfung [dB].
Fig.50: Power and attenuation budgetThe attenuation level must not exceed the power budget, otherwise reliable reception is no longer possible. A reserve as high as >3 dB is recommended (see diagram) to ensure long-term operation for years despite aging effects as sources in the transmitter age and lose power, connectors or splices deteriorate, or connectors become dirty when disconnected for rerouting or testing. If cables are accidentally cut later, a reserve is useful to accommodate splices for reconnection.
Example calculation of power and attenuation budget
In an example calculation, the power and attenuation budget is to be calculated for a transmission link of 2.1 km in length between an EK1501 and an EK1521 with a multimode fiber in the strength 50/125 µm. The two fiber-optic couplers under consideration have the same transceiver. The optical data are given in the technical data for the EK1521.
First of all, the power budget existing between the two couplers must be calculated:
Power budget | |
|---|---|
Parameter | Value |
Minimum output power [50/125 µm] | -23.5 dBm |
Maximum sensitivity | -31 dBm |
Power budget | 7.5 dBm |
In the next step, the attenuation budget, i.e. the attenuation over the entire transmission link, must be calculated. A multimode fiber in the strength 50/125 µm from Beckhoff (ZK1091-1001-xxxx) is used for this example. A maximum attenuation of 0.8 dB/km at a wavelength of 1310 nm is specified in the data sheet for the fiber-optic cable. The cable is connected at both ends via an SC connector. The typical attenuation value of SC connectors is 0.25 dB, but it should nevertheless be checked for the specific application. Three splices were made over the entire link. A typical attenuation of 0.3 dB can be assumed per splice connection; however, the attenuation of a splice is dependent on its quality. The attenuation budget must be calculated from these values in the following.
Attenuation budget | ||
|---|---|---|
Parameter | Number | Value |
Fiber loss attenuation (0.8 dB/km) | 2.1 km | 1.68 dB |
Connector insertion attenuation (0.25 dB) | 2 | 0.5 dB |
Splice insertion attenuation (0.3 dB) | 3 | 0.9 dB |
Attenuation budget |
| 3.08 dB |
If the attenuation budget is now subtracted from the power budget, a power buffer of 4.42 dB results. This is greater than 3 dB and is therefore sufficient as a buffer for most applications, so that an additional splice or slight soiling of the fiber would not lead to failure of the data transmission.
If several values are given for a parameter in the data sheet for transceivers, cables or connectors, the worst value should always be taken and used for the calculation.
For the transmission link under consideration, the bandwidth/length ratio specified in the data sheet for the fiber should always be considered in addition to the attenuation and, as shown above, one should calculate whether the implementation of the length of the transmission link is possible with the desired bandwidth and the fiber.
Overdrive
An optical receiver can not only receive too little light power (and thus cause data errors or bit errors), but also too much, resulting in overdriving with the same immediate consequences and possibly even long-term damage. In addition to the sensitivity of the receiver at low transmission power, compliance with the maximum permissible optical input power must therefore also be checked. Overloading can occur in particular, but not exclusively, with short connections and SFP modules.
The minimum and maximum transmit and receive power of an optical transceiver are usually specified in the technical data.
If the transmit power of the remote station exceeds the maximum permissible receive power of the receiver, an optical attenuator should be used to attenuate the transmit power and prevent the receiver from being overloaded. However, it should be borne in mind that optical components and links age over time, which is why the attenuator should not be set too high.
The connection between an EK1521 and a multimode SFP, operated in the CU1521-0020, is now considered as an example:
Fig.51: Performance curve via the EK1521 vs. CU1521-0020 coupling- Left scale: The maximum permanently permissible optical input power of the EK1521 (green: receiver, Rx) is -14 dBm*) and the maximum transmission power of the SFP (blue: transmitter, Tx) is -8 dBm; it is therefore significantly higher. Damage may occur with direct/short connections.
- The signal must therefore be attenuated by at least 6 dB on the path between the transmitter and receiver to prevent the receiver from overloading. It is also advisable to allow for a reserve of around 2 dB.
- Assume a fiber optic cable length of 2 km at 1.25 dB/km, which results in an attenuation of 2.5 dB*). With two connectors of 0.25 dB*) each, 0.5 dB attenuation is added. The attenuation budget of the transmission path is therefore 3 dB.
- With an attenuation budget of 3 dB and a reserve of 2 dB, an attenuator with 5 dB is therefore inserted in the transmitter-receiver path.
Calculation: AttenuationAttenuator = Attenuationnecessary + Attenuationreserve - Attenuationbudget = 6 dB + 2 dB – 3 dB = 5 dB- Right scale: The power ratio between receivable and actually received optical power, taking into account the transmission path and 5 dB attenuator, is as shown: the attenuated incoming transmission power (blue) is now within the permissible power range of the receiver and is therefore OK.
In some devices, the actual transmit and receive power can be viewed using the SFP diagnostic data (DDM)
Fig.52: Real-time display of Tx/Rx power in the CU1521-0020Note: If the line from the Tx port to the Rx port of the SFP is bridged (loopback), the Tx power transmitted can be compared with the Rx power actually received.
*) Note: The values given are example values. The specific details in the device documentation are decisive.
Evaluation of a fiber-optic transmission link by means of measurement
A fiber-optic transmission link can be described and evaluated with parameters from data sheets. In order to obtain a real result for the attenuation over the entire link, however, the link must be measured using an optical power meter (OPM). The power at the end of the transmission link can be measured with an OPM.
When measuring with an OPM, it is essential to ensure that only the required adapter (FC, SC, …) is screwed to the OPM. If several adapters are screwed above one another to the OPM, the distance between the connector and the detector in the OPM is too large, with the result that lower power values are displayed (greater attenuation than actually exists).

OPM without adapter | OPM with FC adapter screwed on |

OPM with SC adapter screwed on | OPM with FC and SC adapter screwed on - WRONG |