Technical data
Technical data
EK1100-0008
Task in the EtherCAT system
Coupling of EtherCAT Terminals (ELxxxx) to 100BASE-TX EtherCAT networks
Number of EtherCAT Terminals
up to 65535 in the overall system
Data transfer medium
Ethernet 100BASE-TX (at least Ethernet CAT5 cable)
Cable length between 2 Bus Couplers
max. 100 m (100BASE-TX)
Data transfer rates
100 Mbaud
Configuration
not required
Delay
1 µs typ.
Bus interface
2 x M8
Power supply
24 VDC (-15%/+20%)
Current consumption from US
70 mA + (∑ E-bus current/4)
Current consumption from UP
Load
E-bus power supply
max. 2 A (-25 °C ... +55 °C)
max. 1 A (> +55 °C)
Power contacts
max. 24 VDC, max. 10 A
Electrical isolation
500 V (power contact/supply voltage/EtherCAT)
Dimensions (W x H x D)
approx. 44 mm x 100 mm x 68 mm
Weight
approx. 105 g
Permissible ambient temperature range during operation
-25°C ... +60°C
Permissible ambient temperature range during storage
-40°C ... + 85°C
Permissible relative air humidity
95%, no condensation
Mounting
on 35 mm mounting rail according to EN 60715
Enhanced mechanical load capacity
yes, see also Installation instructions for enhanced mechanical load capacity
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP20
Installation position
variable
Approvals / markings*)
CE, EAC, UKCA
ATEX, IECEx, CCC
cULus
Ex markings
Standard
Marking
ATEX
II 3 G Ex nA IIC T4 Gc
II 3 D Ex tc IIIC T135 °C Dc
IECEx
Ex nA IIC T4 Gc