ADS error codes
Error codes are generated in the event of an error during ADS access to an IO-Link device.
The possible error codes are listed in tables C.1 and C.2.
Example of an AdsReturnCode
AdsReturnCode 0x80110700
- 80: Device Application Error (IO-Link Spec),
- 11: Index not Available (IO-Link Spec),
- 0700: General ADS Error
ErrorTypes (IO-Link Spec)
 Incident  |
 Error Code  |
 Additional Code  |
 Name  |
 Definition  |
 Device application error – no details  |
 0x80  |
 0x00  |
 APP_DEV  |
 This ErrorType shall be used if the requested service has been refused by the Device application and no detailed  |
 Index not available  |
 0x80  |
 0x11  |
 IDX_NOTAVAIL  |
 This ErrorType shall be used whenever a read or write access occurs to a not existing Index.  |
 Subindex not available  |
 0x80  |
 0x12  |
 SUBIDX_NOTAVAIL  |
 This ErrorType shall be used whenever a read or write access occurs to a not existing Subindex.  |
 Service temporarily not available  |
 0x80  |
 0x20  |
 SERV_NOTAVAIL  |
 This ErrorType shall be used if a parameter is not accessible for a read or write service due to the current state of the Device application.  |
 Service temporarily not available – local control  |
 0x80  |
 0x21  |
 SERV_NOTAVAIL_LOCCTRL  |
 This ErrorType shall be used if a parameter is not accessible for a read or write service due to an ongoing local operation at the Device (for example operation or parameterization via an on-board Device control panel).  |
 Service temporarily not available – Device control  |
 0x80  |
 0x22  |
 SERV_NOTAVAIL_DEVCTRL  |
 This ErrorType shall be used if a read or write service is not accessible due to a remote triggered state of the device application (for example parameterization during a remote triggered teach-in operation or calibration).  |
 Access denied  |
 0x80  |
 0x23  |
 IDX_NOT_WRITEABLE  |
 This ErrorType shall be used if a write service tries to access a read-only parameter.  |
 Parameter value out of range  |
 0x80  |
 0x30  |
 PAR_VALOUTOFRNG  |
 This ErrorType shall be used for a write service to a parameter outside its permitted range of values.  |
 Parameter value above limit  |
 0x80  |
 0x31  |
 PAR_VALGTLIM  |
 This ErrorType shall be used for a write service to a parameter above its specified value range.  |
 Parameter value below limit  |
 0x80  |
 0x32  |
 PAR_VALLTLIM  |
 This ErrorType shall be used for a write service to a parameter below its specified value range.  |
 Parameter length overrun  |
 0x80  |
 0x33  |
 VAL_LENOVRRUN  |
 This ErrorType shall be used when the content of a write service to a parameter is greater than the parameter specified length. This ErrorType shall also be used, if a data object is too large to be processed by the Device application (for example ISDU buffer restriction).  |
 Parameter length underrun  |
 0x80  |
 0x34  |
 VAL_LENUNDRUN  |
 This ErrorType shall be used when the content of a write service to a parameter is less than the parameter specified length (for example write access of an Unsigned16 value to an Unsigned32 parameter).  |
 Function not available  |
 0x80  |
 0x35  |
 FUNC_NOTAVAIL  |
 This ErrorType shall be used for a write service with a command value not supported by the Device application (for example a SystemCommand with a value not implemented).  |
 Function temporarily unavailable  |
 0x80  |
 0x36  |
 FUNC_UNAVAILTEMP  |
 This ErrorType shall be used for a write service with a command value calling a Device function not available due to the current state of the Device application (for example a SystemCommand).  |
 Invalid parameter set  |
 0x80  |
 0x40  |
 PAR_SETINVALID  |
 This ErrorType shall be used if values sent via single parameter transfer are not consistent with other actual parameter settings (for example overlapping set points for a binary data setting  |
 Inconsistent parameter set  |
 0x80  |
 0x41  |
 PAR_SETINCONSIST  |
 This ErrorType shall be used at the termination of a block parameter transfer with ParamDownloadEnd or ParamDownloadStore if the plausibility check shows inconsistencies  |
 Application not ready  |
 0x80  |
 0x82  |
 APP_DEVNOTRDY  |
 This ErrorType shall be used if a read or write service is refused due to a temporarily unavailable application (for example peripheral controllers during startup).  |
 Vendor specific  |
 0x81  |
 0x00  |
 UNSPECIFIC  |
 This ErrorType will be propagated directly to higher level processing elements as an error (no warning) by the Master.  |
 Vendor specific  |
 0x81  |
 0x01 to 0xFF  |
 VENDOR_SPECIFIC  |
Table C.1 ErrorTypes, IO-Link Spec
Derived ErrorTypes (IO-Link Spec)
 Incident  |
 Error Code  |
 Additional Code  |
 Name  |
 Definition  |
 Master – Communication error  |
 0x10  |
 0x00  |
 COM_ERR  |
 The Master generates a negative service response with this ErrorType if a communication error occurred during a read or write service, for example the SDCI connection is interrupted.  |
 Master – ISDU timeout  |
 0x11  |
 0x00  |
 I-SERVICE_TIMEOUT  |
 The Master generates a negative service response with this ErrorType, if a Read or Write service is pending longer than the specified I-Service timeout in the Master.  |
 Device Event – ISDU error (DL, Error, single shot, 0x5600)  |
 0x11  |
 0x00  |
 I-SERVICE_TIMEOUT  |
 If the Master received an Event with the EventQualifier and the EventCode 0x5600, a negative service response indicating a service timeout is generated and returned to the requester (Master – ISDU timeout).  |
 Device Event – ISDU illegal service primitive (AL, Error, single shot, 0x5800)  |
 0x11  |
 0x00  |
 I-SERVICE_TIMEOUT  |
 If the Master received an Event with the EventQualifier and the EventCode 0x5800, a negative service response indicating a service timeout is generated and returned to the requester (Master – ISDU timeout).  |
 Master – ISDU checksum error  |
 0x56  |
 0x00  |
 M_ ISDU_CHECKSUM  |
 The Master generates a negative service response with this ErrorType, if its data link layer detects an ISDU checksum error.  |
 Master – ISDU illegal service primitive  |
 0x57  |
 0x00  |
 M_ ISDU_ILLEGAL  |
 The Master generates a negative service response with this ErrorType, if its data link layer detects an ISDU illegal service primitive.  |
 Device Event – ISDU buffer overflow (DL, Error, single shot, 0x5200)  |
 0x80  |
 0x33  |
 VAL_LENOVRRUN  |
 If the Master received an Event with the EventQualifier and the EventCode 0x5200, a negative service response indicating a parameter length overrun is generated and returned to the requester (see parameter length overrun)
 Events from legacy Devices shall be redirected in compatibility mode to this derived ErrorType  |
Table C.2 Derived ErrorTypes, IO-Link Spec