Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave:
| UINT32 | RO | 0x02581389 (39326601dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EJ6002 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | 00 |
Index 100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 01 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x177222852 (393357394dec) |
1018:03 | Revision | Revision number of the EtherCAT slave:
| UINT32 | RO | 0x00000000 (0dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave:
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1600 COM RxPDO-Map Outputs Ch.1
1600:0 | COM RxPDO-Map Outputs Ch.1 | PDO Mapping RxPDO 1 | UINT8 | RO | 0x1C (28dec) |
1600:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x01 (Transmit request)) | UINT32 | RO | 0x7000:01, 1 |
1600:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x02 (Receive accepted)) | UINT32 | RO | 0x7000:02, 1 |
1600:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x03 (Init request)) | UINT32 | RO | 0x7000:03, 1 |
1600:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x04 (Send continuous)) | UINT32 | RO | 0x7000:04, 1 |
1600:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1600:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x09 (Output length)) | UINT32 | RO | 0x7000:09, 8 |
1600:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7000:11, 8 |
1600:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7000:12, 8 |
1600:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7000:13, 8 |
1600:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7000:14, 8 |
1600:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7000:15, 8 |
1600:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7000:16, 8 |
1600:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7000:17, 8 |
1600:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7000:18, 8 |
1600:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7000:19, 8 |
1600:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7000:1A, 8 |
1600:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7000:1B, 8 |
1600:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7000:1C, 8 |
1600:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7000:1D, 8 |
1600:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7000:1E, 8 |
1600:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7000:1F, 8 |
1600:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7000:20, 8 |
1600:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7000:21, 8 |
1600:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7000:22, 8 |
1600:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7000:23, 8 |
1600:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7000:24, 8 |
1600:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7000:25, 8 |
1600:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1) entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7000:26, 8 |
Index 1601 COM RxPDO-Map Ext. Outputs Ch.1
1601:0 | COM RxPDO-Map Ext. Outputs Ch.1 | PDO Mapping RxPDO 2 | UINT8 | RO | 0x03 (03dec) |
1601:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7001 (COM Ext. Outputs Ch.1), entry 0x01 (Tx)) | UINT32 | RO | 0x7001:01, 1 |
1601:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7001 (COM Ext. Outputs Ch.1), entry 0x02 (RTS)) | UINT32 | RO | 0x7001:02, 1 |
1601:03 | SubIndex 003 | 3. PDO Mapping entry (14 bits align) | UINT32 | RO | 0x0000:00, 14 |
Index 1602 COM RxPDO-Map Outputs Ch.2
1602:0 | COM RxPDO-Map Outputs Ch.2 | PDO Mapping RxPDO 3 | UINT8 | RO | 0x1C (28dec) |
1602:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x01 (Transmit request)) | UINT32 | RO | 0x7010:01, 1 |
1602:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x02 (Receive accepted)) | UINT32 | RO | 0x7010:02, 1 |
1602:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x03 (Init request)) | UINT32 | RO | 0x7010:03, 1 |
1602:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x04 (Send continuous)) | UINT32 | RO | 0x7010:04, 1 |
1602:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1602:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x09 (Output length)) | UINT32 | RO | 0x7010:09, 8 |
1602:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7010:11, 8 |
1602:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7010:12, 8 |
1602:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7010:13, 8 |
1602:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7010:14, 8 |
1602:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7010:15, 8 |
1602:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7010:16, 8 |
1602:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7010:17, 8 |
1602:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7010:18, 8 |
1602:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7010:19, 8 |
1602:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7010:1A, 8 |
1602:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7010:1B, 8 |
1602:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7010:1C, 8 |
1602:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7010:1D, 8 |
1602:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7010:1E, 8 |
1602:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7010:1F, 8 |
1602:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7010:20, 8 |
1602:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7010:21, 8 |
1602:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7010:22, 8 |
1602:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7010:23, 8 |
1602:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7010:24, 8 |
1602:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7010:25, 8 |
1602:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2) entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7010:26, 8 |
Index 1603 COM RxPDO-Map Ext. Outputs Ch.2
1603:0 | COM RxPDO-Map Ext. Outputs Ch.2 | PDO Mapping RxPDO 4 | UINT8 | RO | 0x03 (03dec) |
1603:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7011 (COM Ext. Outputs Ch.2), entry 0x01 (Tx)) | UINT32 | RO | 0x7011:01, 1 |
1603:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7011 (COM Ext. Outputs Ch.2), entry 0x02 (RTS)) | UINT32 | RO | 0x7011:02, 1 |
1603:03 | SubIndex 003 | 3. PDO Mapping entry (14 bits align) | UINT32 | RO | 0x0000:00, 14 |
Index 1A00 COM TxPDO-Map Inputs Ch.1
1A00:0 | COM TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x1F (31dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x01 (Transmit accepted)) | UINT32 | RO | 06000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x02 (Receive request)) | UINT32 | RO | 06000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x03 (Init accepted)) | UINT32 | RO | 06000:03, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x04 (Buffer full)) | UINT32 | RO | 06000:04, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x05 (Parity error)) | UINT32 | RO | 06000:05, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x06 (Framing error)) | UINT32 | RO | 06000:06, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x07 (Overrun error)) | UINT32 | RO | 06000:07, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x09 (Input length)) | UINT32 | RO | 06000:09, 8 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x11 (Data In 0)) | UINT32 | RO | 06000:11, 8 |
1A00:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x12 (Data In 1)) | UINT32 | RO | 06000:12, 8 |
1A00:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x13 (Data In 2)) | UINT32 | RO | 06000:13, 8 |
1A00:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x14 (Data In 3)) | UINT32 | RO | 06000:14, 8 |
1A00:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x15 (Data In 4)) | UINT32 | RO | 06000:15, 8 |
1A00:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x16 (Data In 5)) | UINT32 | RO | 06000:16, 8 |
1A00:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x17 (Data In 6)) | UINT32 | RO | 06000:17, 8 |
1A00:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x18 (Data In 7)) | UINT32 | RO | 06000:18, 8 |
1A00:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x19 (Data In 8)) | UINT32 | RO | 06000:19, 8 |
1A00:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1A (Data In 9)) | UINT32 | RO | 06000:1A, 8 |
1A00:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1B (Data In 10)) | UINT32 | RO | 06000:1B, 8 |
1A00:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 11)) | UINT32 | RO | 06000:1C, 8 |
1A00:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 12)) | UINT32 | RO | 06000:1D, 8 |
1A00:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1E (Data In 13)) | UINT32 | RO | 06000:1E, 8 |
1A00:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x1F (Data In 14)) | UINT32 | RO | 06000:1F, 8 |
1A00:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x20 (Data In 15)) | UINT32 | RO | 06000:20, 8 |
1A00:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x21 (Data In 16)) | UINT32 | RO | 06000:21, 8 |
1A00:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x22 (Data In 17)) | UINT32 | RO | 06000:22, 8 |
1A00:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x23 (Data In 18)) | UINT32 | RO | 06000:23, 8 |
1A00:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x24 (Data In 19)) | UINT32 | RO | 06000:24, 8 |
1A00:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x25 (Data In 20)) | UINT32 | RO | 06000:25, 8 |
1A00:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x0x6000 (COM Inputs Ch.1), entry 0x26 (Data In 21)) | UINT32 | RO | 06000:26, 8 |
Index 1A01 COM TxPDO-Map Ext. Inputs Ch.1
1A01:0 | COM TxPDO-Map Ext. Inputs Ch.1 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x03 (3dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (COM Ext. Inputs Ch.1), entry 0x01 (Rx)) | UINT32 | RO | 0x6001:01, 1 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6001 (COM Ext. Inputs Ch.1), entry 0x02 (CTS)) | UINT32 | RO | 0x6001:02, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (14 bits align) | UINT32 | RO | 0x0000:00, 14 |
Index 1A02 COM TxPDO-Map Inputs Ch.2
1A02:0 | COM TxPDO-Map Inputs Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x1F (31dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x01 (Transmit accepted)) | UINT32 | RO | 06010:01, 1 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x02 (Receive request)) | UINT32 | RO | 06010:02, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x03 (Init accepted)) | UINT32 | RO | 06010:03, 1 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x04 (Buffer full)) | UINT32 | RO | 06010:04, 1 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x05 (Parity error)) | UINT32 | RO | 06010:05, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x06 (Framing error)) | UINT32 | RO | 06010:06, 1 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x07 (Overrun error)) | UINT32 | RO | 06010:07, 1 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x09 (Input length)) | UINT32 | RO | 06010:09, 8 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x11 (Data In 0)) | UINT32 | RO | 06010:11, 8 |
1A02:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x12 (Data In 1)) | UINT32 | RO | 06010:12, 8 |
1A02:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x13 (Data In 2)) | UINT32 | RO | 06010:13, 8 |
1A02:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x14 (Data In 3)) | UINT32 | RO | 06010:14, 8 |
1A02:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x15 (Data In 4)) | UINT32 | RO | 06010:15, 8 |
1A02:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x16 (Data In 5)) | UINT32 | RO | 06010:16, 8 |
1A02:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x17 (Data In 6)) | UINT32 | RO | 06010:17, 8 |
1A02:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x18 (Data In 7)) | UINT32 | RO | 06010:18, 8 |
1A02:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x19 (Data In 8)) | UINT32 | RO | 06010:19, 8 |
1A02:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1A (Data In 9)) | UINT32 | RO | 06010:1A, 8 |
1A02:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1B (Data In 10)) | UINT32 | RO | 06010:1B, 8 |
1A02:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1C (Data In 11)) | UINT32 | RO | 06010:1C, 8 |
1A02:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1D (Data In 12)) | UINT32 | RO | 06010:1D, 8 |
1A02:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1E (Data In 13)) | UINT32 | RO | 06010:1E, 8 |
1A02:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x1F (Data In 14)) | UINT32 | RO | 06010:1F, 8 |
1A02:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x20 (Data In 15)) | UINT32 | RO | 06010:20, 8 |
1A02:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x21 (Data In 16)) | UINT32 | RO | 06010:21, 8 |
1A02:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x22 (Data In 17)) | UINT32 | RO | 06010:22, 8 |
1A02:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x23 (Data In 18)) | UINT32 | RO | 06010:23, 8 |
1A02:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x24 (Data In 19)) | UINT32 | RO | 06010:24, 8 |
1A02:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x25 (Data In 20)) | UINT32 | RO | 06010:25, 8 |
1A02:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x0x6010 (COM Inputs Ch.2), entry 0x26 (Data In 21)) | UINT32 | RO | 06010:26, 8 |
Index 1A03 COM TxPDO-Map Ext. Inputs Ch.2
1A03:0 | COM TxPDO-Map Ext. Inputs Ch.2 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x03 (3dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (COM Ext. Inputs Ch.2), entry 0x01 (Rx)) | UINT32 | RO | 0x6011:01, 1 |
1A03:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6011 (COM Ext. Inputs Ch.2), entry 0x02 (CTS)) | UINT32 | RO | 0x6011:02, 1 |
1A03:03 | SubIndex 003 | 3. PDO Mapping entry (14 bits align) | UINT32 | RO | 0x0000:00, 14 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RO | 0x00 (0dec) |
1C32:0 | SM output parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0000 (0dec) |
1C32:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x0003D090 (250000dec) |
1C32:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x0001 (1dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00002710 (10000dec) |
1C32:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C32:07 | Minimum delay time | Min. time between SYNC1 event and the reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000384 (900dec) |
1C32:08 | Command | With this entry the real required process data provision time can be measured.
The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Maximum Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | Cycle time (in ns):
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00002710 (10000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time | Min. time between SYNC1 event and the reading of the inputs (in ns, DC mode only) | UINT32 | RO | 0x00000384 (900dec) |
1C33:08 | Command | With this entry the real required process data provision time can be measured.
1C33:09 | Maximum Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
