0x8010 - enhanced operating mode
Index 8010 ENC Settings
8010:0 | ENC Settings | Maximum subindex | UINT8 | RO | 0x21 (33dec) |
8010:01 | Enable C reset | The counter is reset via the C input. | BOOLEAN | RW | 0x00 (0dec) |
8010:02 | Enable extern reset | A counter reset is triggered via the external latch input (24 V). | BOOLEAN | RW | 0x00 (0dec) |
8010:03 | Enable up/down counter | Enables the up/down counter instead of the encoder when the bit is set. | BOOLEAN | RW | 0x00 (0dec) |
8010:04 | Gate polarity | 0: Disable gate | BIT2 | RW | 0x01 (1dec) |
8010:08 | Disable filter | 0: Activates input filter (only inputs A, /A, B, /B, C, /C) | BOOLEAN | RW | 0x01 (1dec) |
8010:0A | Enable micro increments | If DC mode is enabled, the module interpolates micro-increments between the integer encoder increments. The lower 8 bits of the Counter-Value are used for the display. | BOOLEAN | RW | 0x00 (0dec) |
8010:0B | Open circuit detection A | A wire break on the A track is displayed in the index 0x6010:07 and as process data. | BOOLEAN | RW | 0x01 (1dec) |
8010:0C | Open circuit detection B | A wire break on the B track is displayed in the index 0x6010:07 and as process data. | BOOLEAN | RW | 0x01 (1dec) |
8010:0D | Open circuit detection C | A wire break on the C track is displayed in the index 0x6010:07 and as process data. | BOOLEAN | RW | 0x00 (0dec) |
8010:0E | Reversion of rotation | Activates reversion of rotation | BOOLEAN | RW | 0x00 (0dec) |
8010:10 | Extern reset polarity | 0: (Fall) with the falling edge the counter is set to 0 | BIT1 | RW | 0x01 (1dec) |
8010:11 | Frequency window | This is the minimum time over which the frequency is determined. The number of pulses in the timeframe + the following is measured. The maximum waiting time is Frequency Wait Time Index 0x8010:17. The number of pulses is then divided by the actual timeframe size.The determined frequency is output in Frequency scaling index 0x6010:13 and as the process data.The frequency calculation is performed locally and does not use a distributed clocks function. | UINT16 | RW | 0x2710 (10000dec) |
8010:13 | Frequency scaling | Scaling of the frequency measurement (must be divided by this value to obtain the unit in Hz): | UINT16 | RW | 0x0064 (100dec) |
8010:14 | Period scaling | Resolution of the period value in the process data: | UINT16 | RW | 0x0064 (100dec) |
8010:15 | Frequency resolution | Resolution of the frequency measurement: | UINT16 | RW | 0x0064 (100dec) |
8010:16 | Period resolution | Internal resolution of the interval measurement: 100: "100 ns" Period value is a multiple of 100 ns 500: "500 ns" Period value is a multiple of 500 ns | UINT16 | RW | 0x01F4 (500dec) |
8010:17 | Frequency Wait Time | Waiting time [ms] for frequency measurement If the time from Frequency window index 0x8010:11 has elapsed, the system still waits for the next positive edge from track A for the duration specified in Frequency Wait Time. | UINT16 | RW | 0x0640 (1600dec) |
8010:21 | Enable encoder plausibility check | Activation of plausibility check | BOOLEAN | RW | 0x00 (0dec) |