Configuration data
Index 80n0 TC Settings  (for Ch. 1 - 4 (0 ≤ n ≤  3))
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
TC Settings Ch (n+1)
Maximum subindex
UINT8
RO
0x19 (25dec)
80n0:01
Enable user scale
User scaling is enabled.
BOOLEAN
RW
0x00 (0dec)
80n0:02
Presentation
0: Signed presentation, 0.1°C/digit
1: Absolute value with MSB as sign (signed amount representation), 0.1°C/digit
2: High resolution (0.01°C/digit)
BIT3
RW
0x00 (0dec)
80n0:05
Siemens bits
The S5 bits are displayed in the three low-order bits
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
This setting generally activates the basic filters in object 0x80n0:15. These are technically implemented in the ADC and therefore cannot be switched off, even if this object is set to “disabled”.
BOOLEAN
RW
0x01 (1dec)
80n0:0A
Enable user calibration
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
BOOLEAN
RW
0x01 (1dec)
80n0:0C
Coldjunction compensation
0: intern RTD Ch1
1: no
Cold junction compensation is not active
2: Extern process data
Cold junction compensation takes place via the process data (resolution [1/10]°C)
3: intern RTD Ch2
BIT2
RW
0x00 (0dec)
80n0:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
8000:12
User scale gain
Gain of the user scaling.
The gain has a fixed-point representation with a factor of 2-16.
The value 1 corresponds to 65536 (0x00010000)
INT32
RW
0x00010000 (65536dec)
Index (hex)
Meaning
Data type
Flags
Default
80n0:15
Filter settings
This object determines the digital basic filter settings.
The possible settings are numbered consecutively.
UINT16
RW
0x0000 (0dec)
0: 50 Hz (default)
1: 60 Hz
2: 100 Hz
3: 500 Hz
4: 1 kHz
5: 2 kHz
6: 3.75 kHz
7: 7.5 kHz
8: 15 kHz
9: 30 kHz
10: 5 Hz
11:10 Hz
80n0:17
User calibration offset
INT16
RW
0x0000 (0dec)
80n0:18
User calibration gain
UINT16
RW
0xFFFF (65535dec)
80n0:19
TC element
Thermocouple
Implemented temperature range
UINT16
RW
0x0000 (0dec)
0: Type: K -200°C to 1370°C
1: Type: J -100°C to 1200°C
2: Type: L  0°C to 900°C
3: Type: E -100°C to 1000°C
4: Type: T -200°C to 400°C
5: Type: N -100°C to 1300°C
6: Type: U 0°C to 600°C
7: Type: B 200…1820
8: Type: R -50…1767
9: Type: S -50…1760
10: Type: C 0°C to 2320°C
100:  ±30 mV (1 µV resolution)
101:  ±60 mV (2 µV resolution)
102:  ±75 mV (4 µV resolution)
Index 8040 RTD Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8040:0
RTD Settings Ch.1
Max. subindex
UINT8
RO
0x1B (27dec)
8040:19
RTD Element
Permitted values
2: PT1000 (-200 … 850°C)
8: Resistor 1/16 Ohm resolution (0…4095 Ohm)
UINT16
RW
0x0002 (2dec)
8040:1A
Connection technology
Permitted values
0: Two-wire connection
3: not connected
UINT16
RW
0x0000 (0dec)
8040:1B
Wire calibration 1/32 Ohm
Offset-value for calibration of supply lines [1/32] Ohm
UINT16
RW
0x0000 (0dec)
Index 8050 RTD Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8050:0
RTD Settings Ch.1
Max. subindex
UINT8
RO
0x1B (27dec)
8050:19
RTD Element
Permitted values
UINT16
RW
0x0002 (2dec)
8050:1A
Permitted values
3: not connected
UINT16
RW
0x0000 (0dec)
8050:1B
Calibration of supply lines
UINT16
RW
0x0000 (0dec)
Index 8060 TSC Settings
Index (hex)
Meaning
Data type
Flags
Default
8060:0
TSC Settings
Max. subindex
UINT8
RO
0x02 (2dec)
8060:19
Address
TwinSAFE SC address
UINT16
RW
0x0001 (1dec)
8060:1A
Connection Mode
Selection of TwinSAFE SC CRC
Permitted values
UINT32
RW
0x00017B0F (97039dec)
97039
TwinSAFE SC CRC1 master
153375
TwinSAFE SC CRC2 master
204693
TwinSAFE SC CRC3 master
283633
TwinSAFE SC CRC4 master
389589
TwinSAFE SC CRC5 master
419387
TwinSAFE SC CRC6 master
506061
TwinSAFE SC CRC7 master
582077
TwinSAFE SC CRC8 master