Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x012C1389(19665801dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EJ3004, |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | 00 |
Index 100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 01 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | EJ3004: 0x5228BC0B, |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description. | UINT32 | RO | 0x00000000 |
1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0. | UINT32 | RO | 0x00000000 |
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1800 AI TxPDO-Par Standard Ch.1
1800:0 | AI TxPDO-Par Standard Ch.1 | PDO parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1800:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 01 1A |
Index 1801 AI TxPDO-Par Compact Ch.1
1801:0 | AI TxPDO-Par Compact Ch.1 | PDO parameter TxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1801:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 | OCTET-STRING[2] | RO | 00 1A |
Index 1802 AI TxPDO-Par Standard Ch.2
1802:0 | AI TxPDO-Par Standard Ch.2 | PDO parameter TxPDO 3 | UINT8 | RO | 0x06 (6dec) |
1802:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3 | OCTET-STRING[2] | RO | 03 1A |
Index 1803 AI TxPDO-Par Compact Ch.2
1803:0 | AI TxPDO-Par Compact Ch.2 | PDO parameter TxPDO 4 | UINT8 | RO | 0x06 (6dec) |
1803:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4 | OCTET-STRING[2] | RO | 02 1A |
Index 1804 AI TxPDO-Par Standard Ch.3
1804:0 | AI TxPDO-Par Standard Ch.3 | PDO parameter TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1804:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5 | OCTET-STRING[2] | RO | 05 1A |
Index 1805 AI TxPDO-Par Compact Ch.3
1805:0 | AI TxPDO-Par Compact Ch.3 | PDO parameter TxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1805:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6 | OCTET-STRING[2] | RO | 04 1A |
Index 1806 AI TxPDO-Par Standard Ch.4
1806:0 | AI TxPDO-Par Standard Ch.4 | PDO parameter TxPDO 7 | UINT8 | RO | 0x06 (6dec) |
1806:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7 | OCTET-STRING[2] | RO | 07 1A |
Index 1807 AI TxPDO-Par Compact Ch.4
1807:0 | AI TxPDO-Par Compact Ch.4 | PDO parameter TxPDO 8 | UINT8 | RO | 0x06 (6dec) |
1807:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8 | OCTET-STRING[2] | RO | 06 1A |
Index 1808 AI TxPDO-Par Standard Ch.5 (8-channel modules only)
1808:0 | AI TxPDO-Par Standard Ch.5 | PDO parameter TxPDO 9 | UINT8 | RO | 0x06 (6dec) |
1808:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 9 | OCTET-STRING[2] | RO | 09 1A |
Index 1809 AI TxPDO-Par Compact Ch.5 (8-channel modules only)
1809:0 | AI TxPDO-Par Compact Ch.5 | PDO parameter TxPDO 10 | UINT8 | RO | 0x06 (6dec) |
1809:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 10 | OCTET-STRING[2] | RO | 08 1A |
Index 180A AI TxPDO-Par Standard Ch.6 (8-channel modules only)
180A:0 | AI TxPDO-Par Standard Ch.6 | PDO parameter TxPDO 11 | UINT8 | RO | 0x06 (6dec) |
180A:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 11 | OCTET-STRING[2] | RO | 0B 1A |
Index 180B AI TxPDO-Par Compact Ch.6 (8-channel modules only)
180B:0 | AI TxPDO-Par Compact Ch.6 | PDO parameter TxPDO 12 | UINT8 | RO | 0x06 (6dec) |
180B:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 12 | OCTET-STRING[2] | RO | 0A 1A |
Index 180C AI TxPDO-Par Standard Ch.7 (8-channel modules only)
180C:0 | AI TxPDO-Par Standard Ch.7 | PDO parameter TxPDO 13 | UINT8 | RO | 0x06 (6dec) |
180C:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 13 | OCTET-STRING[2] | RO | 0D 1A |
Index 180D AI TxPDO-Par Compact Ch.7 (8-channel modules only)
180D:0 | AI TxPDO-Par Compact Ch.7 | PDO parameter TxPDO 14 | UINT8 | RO | 0x06 (6dec) |
180D:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 14 | OCTET-STRING[2] | RO | 0C 1A |
Index 180E AI TxPDO-Par Standard Ch.8 (8-channel modules only)
180E:0 | AI TxPDO-Par Standard Ch.8 | PDO parameter TxPDO 15 | UINT8 | RO | 0x06 (6dec) |
180E:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 15 | OCTET-STRING[2] | RO | 0F 1A |
Index 180F AI TxPDO-Par Compact Ch.8 (8-channel modules only)
180F:0 | AI TxPDO-Par Compact Ch.8 | PDO parameter TxPDO 16 | UINT8 | RO | 0x06 (6dec) |
180F:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 16 | OCTET-STRING[2] | RO | 0E 1A |
Index 1A00 AI TxPDO-Map Standard Ch.1
1A00:0 | AI TxPDO-Map Standard Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x0A (10dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6000:03, 2 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6000:05, 2 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x07 (ERROR)) | UINT32 | RO | 0x6000:07, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x09 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6000:11, 16 |
Index 1A01 AI TxPDO-Map Compact Ch.1
1A01:0 | AI TxPDO-Map Compact Ch.1 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x01 (1dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6000:11, 16 |
Index 1A02 AI TxPDO-Map Standard Ch.2
1A02:0 | AI TxPDO-Map Standard Ch.2 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x0A (10dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6010:01, 1 |
1A02:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6010:02, 1 |
1A02:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6010:03, 2 |
1A02:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6010:05, 2 |
1A02:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x07 (ERROR)) | UINT32 | RO | 0x6010:07, 1 |
1A02:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A02:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A02:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6010:0F, 1 |
1A02:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
1A02:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A03 AI TxPDO-Map Compact Ch.2
1A03:0 | AI TxPDO-Map Compact Ch.2 | PDO Mapping TxPDO 4 | UINT8 | RO | 0x01 (1dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6010:11, 16 |
Index 1A04 AI TxPDO-Map Standard Ch.3
1A04:0 | AI TxPDO-Map Standard Ch.3 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x0A (10dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6020:01, 1 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6020:02, 1 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6020:03, 2 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6020:05, 2 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x07 (Error)) | UINT32 | RO | 0x6020:07, 1 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6020:0F, 1 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6020:10, 1 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6020:11, 16 |
Index 1A05 AI TxPDO-Map Compact Ch.3
1A05:0 | AI TxPDO-Map Compact Ch.3 | PDO Mapping TxPDO 6 | UINT8 | RO | 0x01 (1dec) |
1A05:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6020:11, 16 |
Index 1A06 AI TxPDO-Map Standard Ch.4
1A06:0 | AI TxPDO-Map Standard Ch.4 | PDO Mapping TxPDO 7 | UINT8 | RO | 0x0A (10dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6030:01, 1 |
1A06:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6030:02, 1 |
1A06:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6030:03, 2 |
1A06:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6030:05, 2 |
1A06:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x05 (Error)) | UINT32 | RO | 0x6030:07, 1 |
1A06:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A06:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A06:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6030:0F, 1 |
1A06:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6030:10, 1 |
1A06:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6030:11, 16 |
Index 1A07 AI TxPDO-Map Compact Ch.4
1A07:0 | AI TxPDO-Map Compact Ch.4 | PDO Mapping TxPDO 8 | UINT8 | RO | 0x01 (1dec) |
1A07:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6030:11, 16 |
Index 1A08 AI TxPDO-Map Standard Ch.5 (8-channel modules only)
1A08:0 | AI TxPDO-Map Standard Ch.5 | PDO Mapping TxPDO 9 | UINT8 | RO | 0x0A (10dec) |
1A08:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6040:01, 1 |
1A08:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6040:02, 1 |
1A08:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6040:03, 2 |
1A08:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6040:05, 2 |
1A08:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x07 (ERROR)) | UINT32 | RO | 0x6040:07, 1 |
1A08:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A08:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A08:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6040:0F, 1 |
1A08:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x09 (TxPDO Toggle)) | UINT32 | RO | 0x6040:10, 1 |
1A08:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6040:11, 16 |
Index 1A09 AI TxPDO-Map Compact Ch.5 (8-channel modules only)
1A09:0 | AI TxPDO-Map Compact Ch.5 | PDO Mapping TxPDO 10 | UINT8 | RO | 0x01 (1dec) |
1A09:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6040 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6040:11, 16 |
Index 1A0A AI TxPDO-Map Standard Ch.6 (8-channel modules only)
1A0A:0 | AI TxPDO-Map Standard Ch.6 | PDO Mapping TxPDO 11 | UINT8 | RO | 0x0A (10dec) |
1A0A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6050:01, 1 |
1A0A:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6050:02, 1 |
1A0A:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6050:03, 2 |
1A0A:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6050:05, 2 |
1A0A:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x07 (ERROR)) | UINT32 | RO | 0x6050:07, 1 |
1A0A:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0A:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0A:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6050:0F, 1 |
1A0A:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6050:10, 1 |
1A0A:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6050:11, 16 |
Index 1A0B AI TxPDO-Map Compact Ch.6 (8-channel modules only)
1A0B:0 | AI TxPDO-Map Compact Ch.6 | PDO Mapping TxPDO 12 | UINT8 | RO | 0x01 (1dec) |
1A0B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6050 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6050:11, 16 |
Index 1A0C AI TxPDO-Map Standard Ch.7 (8-channel modules only)
1A0C:0 | AI TxPDO-Map Standard Ch.7 | PDO Mapping TxPDO 13 | UINT8 | RO | 0x0A (10dec) |
1A0C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6060:01, 1 |
1A0C:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6060:02, 1 |
1A0C:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6060:03, 2 |
1A0C:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6060:05, 2 |
1A0C:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x07 (Error)) | UINT32 | RO | 0x6060:07, 1 |
1A0C:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0C:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0C:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6060:0F, 1 |
1A0C:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6060:10, 1 |
1A0C:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6060:11, 16 |
Index 1A0D AI TxPDO-Map Compact Ch.7 (8-channel modules only)
1A0D:0 | AI TxPDO-Map Compact Ch.7 | PDO Mapping TxPDO 14 | UINT8 | RO | 0x01 (1dec) |
1A0D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6060 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6060:11, 16 |
Index 1A0E AI TxPDO-Map Standard Ch.8 (8-channel modules only)
1A0E:0 | AI TxPDO-Map Standard Ch.8 | PDO Mapping TxPDO 15 | UINT8 | RO | 0x0A (10dec) |
1A0E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x01 (Underrange)) | UINT32 | RO | 0x6070:01, 1 |
1A0E:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x02 (Overrange)) | UINT32 | RO | 0x6070:02, 1 |
1A0E:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6070:03, 2 |
1A0E:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6070:05, 2 |
1A0E:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x05 (Error)) | UINT32 | RO | 0x6070:07, 1 |
1A0E:06 | SubIndex 006 | 6. PDO Mapping entry (1 bit align) | UINT32 | RO | 0x0000:00, 1 |
1A0E:07 | SubIndex 007 | 7. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A0E:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6070:0F, 1 |
1A0E:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6070:10, 1 |
1A0E:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6070:11, 16 |
Index 1A0F AI TxPDO-Map Compact Ch.8 (8-channel modules only)
1A0F:0 | AI TxPDO-Map Compact Ch.4 | PDO Mapping TxPDO 8 | UINT8 | RO | 0x01 (1dec) |
1A0F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6070 (AI Inputs), entry 0x11 (Value)) | UINT32 | RO | 0x6070:11, 16 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
Index 1C13 TxPDO assign
For operation on masters other than TwinCAT it must be ensured that the channels are entered in the PDO assignment (“TxPDO assign”, object 0x1C13) successively.
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x08 (8dec) |
1C13:01 | SubIndex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | SubIndex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A02 (6658dec) |
1C13:03 | SubIndex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A04 (6660dec) |
1C13:04 | SubIndex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A06 (6662dec) |
1C13:05* | SubIndex 005 | 5. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A08 (6664dec) |
1C13:06* | SubIndex 006 | 6. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A0A (6666dec) |
1C13:07* | SubIndex 007 | 7. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A0C (6668dec) |
1C13:08* | SubIndex 008 | 8. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A0E (6670dec) |
* 8-channel modules only
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0xC003 (49155dec) |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x0000FDE8 (65000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time | Minimum time between Sync-1 Event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:08 | Command | With this entry the real required process data provision time can be measured.
The entries 0x1C33:03, 0x1C33:06, 1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |