Technical data
General | |
Number of channels | Total | 2 |
Internal communication protocol | EtherCAT |
Motion interface | Operation without fan | Operation with fan |
Number of channels | 2 | |
Load type | stepper motor, unipolar or bipolar | |
Load supply | Input voltage | 8…48 V DC | |
Output current | Rated current | max. 6 A | max. 10 A |
Output current | Rated current (per channel) | max. 5 A | max. 6 A |
Step frequency | max. 16,000 full steps/s | |
Microstepping | 16,384 intermediate steps per full step | |
Frequency | PWM | 16 kHz | |
Frequency | Current controller | 32 kHz | |
Frequency | Position controller | 16 kHz | |
Frequency | Speed controller | 16 kHz | |
STO | no | |
SS1 | no | |
Safe Motion | no | |
Chopper resistance | external, with EL9576 | |
Position interface | |
Function | motor position feedback |
Sensor type | incremental encoder |
Signal range | 5 V differential, single-ended/open collector |
Resolution | Process data (position) | 32 bit |
Sensor supply | Output voltage | 5 V |
Quadrature decoder | yes |
RS422 | |
Encoder connection | differential A, B, C |
Input frequency | max. 400,000 increments/s with 4-fold evaluation |
Wire break detection | no |
TTL | |
Encoder connection | single-ended connection: A, B, C |
Open collector | |
Encoder connection | open collector connection: A, B, C |
Digital input Standard digital | Positive switching | |
Number of channels | 4 |
Function | touch probe |
Connection technology | 1-wire, 2-wire, 3-wire |
Signal range | Nominal | 24 V DC |
Signal voltage “0” | max. 1.8 V DC |
Signal voltage “1” | min. 3 V DC |
Input current | typ. 1.75 mA |
Cable length | Sensor cable | max. 30 m |
Digital output Standard digital | Positive switching | |
Function | motor holding brake |
Load type | resistive, inductive |
Connection technology | 2-wire |
Signal range | Technical | 20.4…28.8 V DC |
Output current | max. 0.5 A |
Short-circuit proof | yes |
Short-circuit current limit | typ. < 2 A |
Output stage | push |
Switching-off energy | Inductive | no |
XFC |
Distributed clocks | yes |
Distributed clocks | Accuracy | < 1 µs |
Distributed clocks | Scope | 64 bit |
Timestamp | yes |
Timestamp | Accuracy | < 1 µs |
Timestamp | Resolution | 1 ns |
Oversampling | no |
Supply and electrical isolation | |
Electronics | Supply voltage | via E-bus |
E-bus | Current consumption | typ. 175 mA |
Power contacts | Input voltage | 24 V DC (-15%, +20%) |
Power contacts | Current carrying capacity | max. 10 A |
Power contacts | Current consumption | load-dependent |
Power contacts | Output voltage | corresponds to Power contacts | Input voltage |
Electrical isolation | Channel/channel | no |
Electrical isolation | Channel/bus | functional, 707 V DC (type test) |
Environmental conditions | |
Operating temperature | 0…55°C |
Storage temperature | -25…+85°C |
Relative humidity | 95%, no condensation |
Standards and approvals | |
Vibration resistance | conforms to EN 60068-2-6 |
Shock resistance | conforms to EN 60068-2-27 |
EMC immunity | conforms to EN 61000-6-2 |
EMC emission | conforms to EN 61000-6-4 |
Markings | CE |
Housing data | ED-24-2x16pin |
Weight | approx. 100 g |
Protection rating | IP20 |
Material | polycarbonate |
Dimensions | Width (single) | 27 mm |
Dimensions | Width (stacked) | 24 mm |
Dimensions | Height | 100 mm |
Dimensions | Depth | 65 mm |
Installation | Terminal/back wall | DIN rail, 35 mm (EN 60715) |
Installation | Terminal/terminal | double slot and key connection |
Pluggable wiring level | no |
Connection mechanism | push-in |
Connection cross-section | Solid wire | 0.08…1.5 mm² |
Connection cross-section | Stranded wire | 0.25…1.5 mm² |
Connection cross-section | With ferrule | 0.14…0.75 mm² |
Connection cross-section AWG | Solid wire | AWG28…16 |
Connection cross-section AWG | Stranded wire | AWG22…16 |
Connection cross-section AWG | With ferrule | AWG26…19 |
Stripping length | 8…9 mm |
Power contact | "+" (left) | yes |
Power contact | "+" (right) | yes |
Power contact | "-" (left) | yes |
Power contact | "-" (right) | yes |
Power contact | "⏚" (left) | no |
Power contact | "⏚" (right) | no |
Insertion lock for power contact "⏚" | yes |