Diag Messages
The terminal provides the following diagnostic messages:
Diag Code
Meaning
TwinCAT Message
Troubleshooting
#x0001
no error
no error
#x1180
Supply voltage ok
Supply voltage ok
#x1707
Channel is not in overload anymore
#x1708
Channel %d is not in overload anymore
#x170E
No overtemperature anymore
#x170F
No overtemperature on channel %d anymore
#x1710
Full voltage range is available again
#x4101
Terminal Overtemperature
Device is too warm internally, but continues to work, ensure cooling
#x4102
Overtemperature on channel %d
#x4710
More than four channels configured for current output, voltage output is limited to ±5 V
If > ±5 V is required on the U channels, other outputs/devices must be used to output the current values.
#x8144
Hardware fault %d
Hardware fault %d
Check load, measure output function externally, contact support if necessary
#x8601
Supply voltage too low
Check voltage of Up power contacts
#x8707
Channel overload (Channel %d)
Check wiring and load, possibly short circuit/OpenLoad?
#x870A
Range error of channel %d
External voltage applied to the channel?
Diag Messages 1:
Fig.32: Display in TwinCAT 3.1
The error states are expressed as follows
Error
PDO
Status.Overrange
Status.Underrange
PDO
Status.Error
(channel by channel)
PDO
Status.Warning
DiagMsg
Error LED
Supply UP (power contacts) too low/too high
No
No
No
Yes
All channels
Output channel overtemperature
No
No
Yes
Yes
No
Output channel overload 1)
No
Yes
No
Yes
Yes
Output channel above/below limiter
Yes
Yes
Yes
No
Yes
Device overtemperature
No
no
All channels
yes
No
1) Probably short circuit at voltage output and setpoint <> 0 V, probably wire break at current output and setpoint <> 0 mA