Connection
Risk of injury through electric shock and damage to the device! Bring the bus terminal system into a safe, de-energized state before beginning to mount, disassemble, or wire the bus terminals! |
Notice | |
Cable lengths > 30 m For cable lengths > 30 m, suitable overvoltage protection (surge protection) must be provided (e g. EL9540-0010) if corresponding interference could affect the signal cable. |
Terminal point | Description | Internally connected with connection | Max. current carrying capacity*) | |
Abbreviation | No. | |||
Ch1 analog output | 1 | Voltage/current output, channel 1 | – | overload protected |
Ch2 analog output | 2 | Voltage/current output, channel 2 | – | overload protected |
Ch3 analog output | 2 | Voltage/current output, channel 3 | – | overload protected |
Ch4 analog output | 2 | Voltage/current output, channel 4 | – | overload protected |
+24 V DC | 5 | +24 V | 6, 7, 8 +24 V power contact | 1 A |
+24 V DC | 6 | +24 V | 5, 7, 8 +24 V power contact | 1 A |
+24 V DC | 7 | +24 V | 5, 6, 8 +24 V power contact | 1 A |
+24 V DC | 8 | +24 V | 5, 6, 7, +24 V power contact | 1 A |
GND | 9 | Analog ground (reference potential for Ch1…Ch4) | 10, 11, 12 | 100 mA**) |
GND | 10 | Analog ground (reference potential for Ch1…Ch4) | 9, 11, 12 | 100 mA**) |
GND | 11 | Analog ground (reference potential for Ch1…Ch4) | 9, 10, 12 | 100 mA**) |
GND | 12 | Analog ground (reference potential for Ch1…Ch4) | 9, 10, 11 | 100 mA**) |
0 V | 13 | 0 V | 14, 15, 16, 0 V power contact | 1 A |
0 V | 14 | 0 V | 13, 15, 16, 0 V power contact | 1 A |
0 V | 15 | 0 V | 13, 14, 16, 0 V power contact | 1 A |
0 V | 16 | 0 V | 13, 14, 15, 0 V power contact | 1 A |
*) Constant current; short-term higher currents are to be avoided and can lead to thermal overload (damage) | ||||
Voltage output 0…10 V/-10…+10 V
- 2-wire: 2-pin voltage output;
- 4-wire: with additional 24 V supply for the actuator
Current output -20/0/+4…+20 mA
- 2-wire: 2-pin current output;