Connection
WARNING
Risk of electric shock and damage of device!
Bring the bus terminal system into a safe, powered down state before starting installation, disassembly or wiring of the bus terminals!
Connection 1:Fig.1: ED4072
Notice
Cable lengths > 30 m
For cable lengths > 30 m, suitable overvoltage protection (Surge-Protection) must be provided (e g. EL9540-0010) if corresponding interference could affect the signal cable.
Terminal point
Internally connected with connection
Max. current carrying capacity *)
Abbreviation
No.
Ch1 analog output
1
Voltage/current output, channel 1
overload protected
Ch2 analog output
2
Voltage/current output, channel 2
overload protected
n.c.
3
n.c.
4
+24 V DC
5
+24 V
6; 7, +24 V power contact
1 A
+24 V DC
6
+24 V
5, 7, +24 V power contact
1 A
+24 V DC
7
+24 V
5, 6, +24 V power contact
1 A
Shield
8
Shield connection
16
1 A ***)
GND
9
Analog ground (reference potential for Ch1 … Ch2)
10
100 mA **)
GND
10
9
100 mA **)
n.c.
11
n.c.
12
0 V
13
0 V
14, 15, 0 V power contact
1 A
0 V
14
0 V
13, 15, 0 V power contact
1 A
0 V
15
0 V
13, 14, 0 V power contact
1 A
Shield
16
Shield connection
8
1 A ***)
*) Constant current; short-term higher currents are to be avoided and can lead to thermal overload (damage).
**) The "GND" potential is internally coupled to the "0 V" potential, but is subject to a reduced current carrying capacity.
***) The connection point connects directly to the DIN rail contact.
Shield connections should generally be de-energized (DC)! See analog technical information in the Beckhoff analog manual.
If possible, an external shield connection, e.g. via Beckhoff ZB8511 or similar, is preferable.
Voltage output 0 … 10 V / -10 … +10 V
Connection 2:Fig.2: Connection example ED4072, voltage output, 2-/4-wire
Current output -20 / 0 / +4 … +20 mA
Connection 3:Fig.3: Connection example ED4072, current output, 2-/4-wire