Standard objects
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: the low word contains the used CoE profile (5001). The high word contains the module profile according to the modular device profile.
UINT32
RO
0x01901389 (26219401dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EL407x
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
00
Index 100B Bootloader version
Index (hex)
Meaning
Data type
Flags
Default
100B:0
Bootloader version
Bootloader version
STRING
RO
n/a
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID for the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x0FEE3052 (267268178dec)
1018:03
Revision
Revision number of the EtherCAT slave; the low word (bit 0–15) indicates the special terminal number, the high word (bit 16–31) refers to the device description
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the low byte (bit 0–7) of the low word contains the year of production, the high byte (bit 8–15) of the low word contains the week of production, the high word (bit 16–31) is 0
UINT32
RO
0x00000000 (0dec)
Index 10E2 Manufacturer-specific Identification Code*)
Index (hex)
Meaning
Data type
Flags
Default
10E2:0
UINT8
RO
0x01 (1dec)
10E2:01
SubIndex 001
reserved
STRING
RO
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 10F3 Diagnosis History
Index (hex)
Meaning
Data type
Flags
Default
10F3:0
Diagnosis History
Maximum subindex
UINT8
RO
0x15 (21dec)
10F3:01
Maximum Messages
Maximum number of stored messages
A maximum of 16 messages can be stored.
UINT8
RO
0x00 (0dec)
10F3:02
Newest Message
Subindex of the latest message
UINT8
RO
0x00 (0dec)
10F3:03
Newest Acknowledged Message
Subindex of the last acknowledged message
UINT8
RW
0x00 (0dec)
10F3:04
New Messages Available
Indicates that a new message is available.
BOOLEAN
RO
0x00 (0dec)
10F3:05
Flags
not used
UINT16
RW
0x0000 (0dec)
10F3:06
Diagnosis Message 001
Message 1
OCTET STRING[24]
RO
{0}
10F3:15
Diagnosis Message 016
Message 16
OCTET STRING[24]
RO
{0}
Index 10F8 Timestamp Object
Index (hex)
Meaning
Data type
Flags
Default
10F8:0
Timestamp Object
Timestamp Object [ns]
For SM synchronous operation: Time since power-on
For DC synchronous operation: copy of the DC time
Time can be used by the device e.g. for timestamps of the DiagMessage
UINT64
RO
Index 1420 AO RxPDO Par Standard (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1420:0
Ch.1
PDO Parameter RxPDO 33
UINT8
RO
0x06 (6dec)
1420:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 33
OCTET STRING[2]
RO
22 16
Index 1422 AO RxPDO Par Standard (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1422:0
AO RxPDO Par Standard (Real32) Ch. 1
PDO Parameter RxPDO 35
UINT8
RO
0x06 (6dec)
1422:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 35
OCTET STRING[2]
RO
20 16
Index 1444 AO RxPDO Par Standard (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1444:0
PDO Parameter RxPDO 69
UINT8
RO
0x06 (6dec)
1444:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 69
OCTET STRING[2]
RO
46 16
Index 1446 AO RxPDO Par Standard (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1446:0
PDO Parameter RxPDO 71
UINT8
RO
0x06 (6dec)
1446:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 71
OCTET STRING[2]
RO
44 16
Index 1468 AO RxPDO Par Standard (INT16) Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
1468:0
PDO Parameter RxPDO 105
UINT8
RO
0x06 (6dec)
1468:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 105
OCTET STRING[2]
RO
6A 16
*) EL4074, EL4078 only
Index 146A AO RxPDO Par Standard (Real32) Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
146A:0
PDO Parameter RxPDO 107
UINT8
RO
0x06 (6dec)
146A:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 107
OCTET STRING[2]
RO
68 16
Index 148C AO RxPDO Par Standard (INT16) Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
148C:0
PDO Parameter RxPDO 141
UINT8
RO
0x06 (6dec)
148C:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 141
OCTET STRING[2]
RO
8E 16
Index 148E AO RxPDO Par Standard (Real32) Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
148E:0
PDO Parameter RxPDO 143
UINT8
RO
0x06 (6dec)
148E:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 143
OCTET STRING[2]
RO
8C 16
Index 14B0 AO RxPDO Par Standard (INT16) Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
14B0:0
PDO Parameter RxPDO 177
UINT8
RO
0x06 (6dec)
14B00:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 177
OCTET STRING[2]
RO
B2 16
*) EL4078 only
Index 14B2 AO RxPDO Par Standard (Real32) Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
14B2:0
PDO Parameter RxPDO 179
UINT8
RO
0x06 (6dec)
14B2:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 179
OCTET STRING[2]
RO
B0 16
*) EL4078 only
Index 14D4 AO RxPDO Par Standard (INT16) Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
14D4:0
PDO Parameter RxPDO 213
UINT8
RO
0x06 (6dec)
14D4:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 213
OCTET STRING[2]
RO
D6 16
*) EL4078 only
Index 14D6 AO RxPDO Par Standard (Real32) Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
14D6:0
PDO Parameter RxPDO 215
UINT8
RO
0x06 (6dec)
14D6:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 215
OCTET STRING[2]
RO
D4 16
*) EL4078 only
Index 14F8 AO RxPDO Par Standard (INT16) Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
14F8:0
PDO Parameter RxPDO 249
UINT8
RO
0x06 (6dec)
14F8:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 249
OCTET STRING[2]
RO
FA 16
*) EL4078 only
Index 14FA AO RxPDO Par Standard (Real32) Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
14FA:0
PDO Parameter RxPDO 251
UINT8
RO
0x06 (6dec)
14FA:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 251
OCTET STRING[2]
RO
F8 16
*) EL4078 only
Index 151C AO RxPDO Par Standard (INT16) Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
151C:0
PDO Parameter RxPDO 285
UINT8
RO
0x06 (6dec)
151C:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 285
OCTET STRING[2]
RO
1E 17
*) EL4078 only
Index 151E AO RxPDO Par Standard (Real32) Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
151E:0
PDO Parameter RxPDO 287
UINT8
RO
0x06 (6dec)
151E:06
Exclude RxPDOs
Specifies the RxPDOs (index of RxPDO mapping objects) that may not be transferred together with RxPDO 287
OCTET STRING[2]
RO
1C 17
*) EL4078 only
Index 1620 AO RxPDO Map Standard (INT16) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1620:0
PDO Mapping RxPDO 33
UINT8
RO
0x01 (1dec)
1620:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7000 (AO Outputs Ch.1), entry 0x11 (Value))
UINT32
RO
0x7000:11, 16
Index 1622 AO RxPDO Map Standard (Real32) Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1622:0
PDO Mapping RxPDO 35
UINT8
RO
0x01 (1dec)
1622:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7000 (AO Outputs Ch.1), entry 0x13 (Value (Real32)))
UINT32
RO
0x7000:13, 32
Index 1623 AO RxPDO Map Cycle Counter Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1623:0
PDO Mapping RxPDO 36
UINT8
RO
0x01 (1dec)
1623:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7000 (AO Outputs Ch.1), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7000:14, 16
Index 1644 AO RxPDO Map Standard (INT16) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1644:0
PDO Mapping RxPDO 69
UINT8
RO
0x01 (1dec)
1644:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7010 (AO Outputs Ch.2), entry 0x11 (Value))
UINT32
RO
0x7010:11, 16
Index 1646 AO RxPDO Map Standard (Real32) Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1646:0
PDO Mapping RxPDO 71
UINT8
RO
0x01 (1dec)
1646:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7010 (AO Outputs Ch.2), entry 0x13 (Value (Real32)))
UINT32
RO
0x7010:13, 32
Index 1647 AO RxPDO Map Cycle Counter Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1647:0
PDO Mapping RxPDO 72
UINT8
RO
0x01 (1dec)
1647:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7010 (AO Outputs Ch.2), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7010:14, 16
Index 1668 AO RxPDO Map Standard (INT16) Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
1668:0
PDO Mapping RxPDO 105
UINT8
RO
0x01 (1dec)
1668:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7020 (AO Outputs Ch.3), entry 0x11 (Value))
UINT32
RO
0x7020:11, 16
Index 166A AO RxPDO Map Standard (Real32) Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
166A:0
PDO Mapping RxPDO 107
UINT8
RO
0x01 (1dec)
166A:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7020 (AO Outputs Ch.3), entry 0x13 (Value (Real32)))
UINT32
RO
0x7020:13, 32
Index 166B AO RxPDO Map Cycle Counter Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
166B:0
PDO Mapping RxPDO 108
UINT8
RO
0x01 (1dec)
166B:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7020 (AO Outputs Ch.3), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7020:14, 16
Index 168C AO RxPDO Map Standard (INT16) Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
168C:0
PDO Mapping RxPDO 141
UINT8
RO
0x01 (1dec)
168C:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7030 (AO Outputs Ch.4), entry 0x11 (Value))
UINT32
RO
0x7030:11, 16
Index 168E AO RxPDO Map Standard (Real32) Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
168E:0
PDO Mapping RxPDO 143
UINT8
RO
0x01 (1dec)
168E:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7030 (AO Outputs Ch.4), entry 0x13 (Value (Real32)))
UINT32
RO
0x7030:13, 32
Index 168F AO RxPDO Map Cycle Counter Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
168F:0
PDO Mapping RxPDO 144
UINT8
RO
0x01 (1dec)
168F:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7030 (AO Outputs Ch.4), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7030:14, 16
Index 16B0 AO RxPDO Map Standard (INT16) Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
16B0:0
PDO Mapping RxPDO 177
UINT8
RO
0x01 (1dec)
16B0:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7040 (AO Outputs Ch.5), entry 0x11 (Value))
UINT32
RO
0x7040:11, 16
*) EL4078 only
Index 16B2 AO RxPDO Map Standard (Real32) Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
16B2:0
PDO Mapping RxPDO 179
UINT8
RO
0x01 (1dec)
16B2:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7040 (AO Outputs Ch.5), entry 0x13 (Value (Real32)))
UINT32
RO
0x7040:13, 32
*) EL4078 only
Index 16B3 AO RxPDO Map Cycle Counter Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
16B3:0
PDO Mapping RxPDO 180
UINT8
RO
0x01 (1dec)
16B3:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7040 (AO Outputs Ch.5), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7040:14, 16
*) EL4078 only
Index 16D4 AO RxPDO Map Standard (INT16) Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
16D4:0
PDO Mapping RxPDO 213
UINT8
RO
0x01 (1dec)
16D4:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7050 (AO Outputs Ch.6), entry 0x11 (Value))
UINT32
RO
0x7050:11, 16
*) EL4078 only
Index 16D6 AO RxPDO Map Standard (Real32) Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
16D6:0
PDO Mapping RxPDO 215
UINT8
RO
0x01 (1dec)
16D6:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7050 (AO Outputs Ch.6), entry 0x13 (Value (Real32)))
UINT32
RO
0x7050:13, 32
*) EL4078 only
Index 16D7 AO RxPDO Map Cycle Counter Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
16D7:0
PDO Mapping RxPDO 216
UINT8
RO
0x01 (1dec)
16D7:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7050 (AO Outputs Ch.6), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7050:14, 16
*) EL4078 only
Index 16F8 AO RxPDO Map Standard (INT16) Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
16F8:0
PDO Mapping RxPDO 249
UINT8
RO
0x01 (1dec)
16F8:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7060 (AO Outputs Ch.7), entry 0x11 (Value))
UINT32
RO
0x7060:11, 16
*) EL4078 only
Index 16FA AO RxPDO Map Standard (Real32) Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
16FA:0
PDO Mapping RxPDO 251
UINT8
RO
0x01 (1dec)
16FA:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7060 (AO Outputs Ch.7), entry 0x13 (Value (Real32)))
UINT32
RO
0x7060:13, 32
*) EL4078 only
Index 16FB AO RxPDO Map Cycle Counter Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
16FB:0
PDO Mapping RxPDO 252
UINT8
RO
0x01 (1dec)
16FB:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7060 (AO Outputs Ch.7), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7060:14, 16
*) EL4078 only
Index 171C AO RxPDO Map Standard (INT16) Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
171C:0
PDO Mapping RxPDO 285
UINT8
RO
0x01 (1dec)
171C:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7070 (AO Outputs Ch.8), entry 0x11 (Value))
UINT32
RO
0x7070:11, 16
*) EL4078 only
Index 171E AO RxPDO Map Standard (Real32) Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
171E:0
PDO Mapping RxPDO 287
UINT8
RO
0x01 (1dec)
171E:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7070 (AO Outputs Ch.8), entry 0x13 (Value (Real32)))
UINT32
RO
0x7070:13, 32
*) EL4078 only
Index 171F AO RxPDO Map Cycle Counter Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
171F:0
PDO Mapping RxPDO 288
UINT8
RO
0x01 (1dec)
171F:01
SubIndex 001
PDO Mapping entry no. 1 (object 0x7070 (AO Outputs Ch.8), entry 0x14 (Output Cycle Counter))
UINT32
RO
0x7070:14, 16
*) EL4078 only
Index 1A20 AO TxPDO Map Status Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A20:0
PDO Mapping TxPDO 33
UINT8
RO
0x08 (8dec)
1A20:01
SubIndex 001
PDO Mapping entry no. 1 (1 bits align)
UINT32
RO
0x0000:00, 1
1A20:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6000 (AO Inputs Ch.1), entry 0x02 (Output Overload))
UINT32
RO
0x6000:02, 1
1A20:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6000 (AO Inputs Ch.1), entry 0x03 (Underrange))
UINT32
RO
0x6000:03, 1
1A20:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6000 (AO Inputs Ch.1), entry 0x04 (Overrange))
UINT32
RO
0x6000:04, 1
1A20:05
SubIndex 005
PDO Mapping entry no. 5 (1 bits align)
UINT32
RO
0x0000:00, 1
1A20:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6000 (AO Inputs Ch.1), entry 0x06 (Warning))
UINT32
RO
0x6000:06, 1
1A20:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6000 (AO Inputs Ch.1), entry 0x07 (Error))
UINT32
RO
0x6000:07, 1
1A20:08
SubIndex 008
PDO Mapping entry no. 8 (9 bits align)
UINT32
RO
0x0000:00, 9
Index 1A41 AO TxPDO Map Status Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A41:0
PDO Mapping TxPDO 66
UINT8
RO
0x08 (8dec)
1A41:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1A41:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6010 (AO Inputs Ch.2), entry 0x02 (Output Overload))
UINT32
RO
0x6010:02, 1
1A41:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6010 (AO Inputs Ch.2), entry 0x03 (Underrange))
UINT32
RO
0x6010:03, 1
1A41:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6010 (AO Inputs Ch.2), entry 0x04 (Overrange))
UINT32
RO
0x6010:04, 1
1A41:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1A41:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6010 (AO Inputs Ch.2), entry 0x06 (Warning))
UINT32
RO
0x6010:06, 1
1A41:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6010 (AO Inputs Ch.2), entry 0x07 (Error))
UINT32
RO
0x6010:07, 1
1A41:08
SubIndex 008
UINT32
RO
0x0000:00, 9
Index 1A62 AO TxPDO Map Status Ch.3*)
Index (hex)
Meaning
Data type
Flags
Default
1A62:0
PDO Mapping TxPDO 99
UINT8
RO
0x08 (8dec)
1A62:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1A62:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6020 (AO Inputs Ch.3), entry 0x02 (Output Overload))
UINT32
RO
0x6020:02, 1
1A62:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6020 (AO Inputs Ch.3), entry 0x03 (Underrange))
UINT32
RO
0x6020:03, 1
1A62:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6020 (AO Inputs Ch.3), entry 0x04 (Overrange))
UINT32
RO
0x6020:04, 1
1A62:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1A62:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6020 (AO Inputs Ch.3), entry 0x06 (Warning))
UINT32
RO
0x6020:06, 1
1A62:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6020 (AO Inputs Ch.3), entry 0x07 (Error))
UINT32
RO
0x6020:07, 1
1A62:08
SubIndex 008
UINT32
RO
0x0000:00, 9
Index 1A83 AO TxPDO Map Status Ch.4*)
Index (hex)
Meaning
Data type
Flags
Default
1A83:0
PDO Mapping TxPDO 132
UINT8
RO
0x08 (8dec)
1A83:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1A83:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6030 (AO Inputs Ch.4), entry 0x02 (Output Overload))
UINT32
RO
0x6030:02, 1
1A83:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6030 (AO Inputs Ch.4), entry 0x03 (Underrange))
UINT32
RO
0x6030:03, 1
1A83:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6030 (AO Inputs Ch.4), entry 0x04 (Overrange))
UINT32
RO
0x6030:04, 1
1A83:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1A83:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6030 (AO Inputs Ch.4), entry 0x06 (Warning))
UINT32
RO
0x6030:06, 1
1A83:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6030 (AO Inputs Ch.4), entry 0x07 (Error))
UINT32
RO
0x6030:07, 1
1A83:08
SubIndex 008
UINT32
RO
0x0000:00, 9
Index 1AA4 AO TxPDO Map Status Ch.5*)
Index (hex)
Meaning
Data type
Flags
Default
1AA4:0
PDO Mapping TxPDO 165
UINT8
RO
0x08 (8dec)
1AA4:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1AA4:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6040 (AO Inputs Ch.5), entry 0x02 (Output Overload))
UINT32
RO
0x6040:02, 1
1AA4:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6040 (AO Inputs Ch.5), entry 0x03 (Underrange))
UINT32
RO
0x6040:03, 1
1AA4:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6040 (AO Inputs Ch.5), entry 0x04 (Overrange))
UINT32
RO
0x6040:04, 1
1AA4:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1AA4:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6040 (AO Inputs Ch.5), entry 0x06 (Warning))
UINT32
RO
0x6040:06, 1
1AA4:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6040 (AO Inputs Ch.5), entry 0x07 (Error))
UINT32
RO
0x6040:07, 1
1AA4:08
SubIndex 008
UINT32
RO
0x0000:00, 9
*) EL4078 only
Index 1AC5 AO TxPDO Map Status Ch.6*)
Index (hex)
Meaning
Data type
Flags
Default
1AC5:0
PDO Mapping TxPDO 198
UINT8
RO
0x08 (8dec)
1AC5:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1AC5:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6050 (AO Inputs Ch.6), entry 0x02 (Output Overload))
UINT32
RO
0x6050:02, 1
1AC5:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6050 (AO Inputs Ch.6), entry 0x03 (Underrange))
UINT32
RO
0x6050:03, 1
1AC5:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6050 (AO Inputs Ch.6), entry 0x04 (Overrange))
UINT32
RO
0x6050:04, 1
1AC5:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1AC5:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6050 (AO Inputs Ch.6), entry 0x06 (Warning))
UINT32
RO
0x6050:06, 1
1AC5:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6050 (AO Inputs Ch.6), entry 0x07 (Error))
UINT32
RO
0x6050:07, 1
1AC5:08
SubIndex 008
UINT32
RO
0x0000:00, 9
*) EL4078 only
Index 1AE6 AO TxPDO Map Status Ch.7*)
Index (hex)
Meaning
Data type
Flags
Default
1AE6:0
PDO Mapping TxPDO 231
UINT8
RO
0x08 (8dec)
1AE6:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1AE6:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6060 (AO Inputs Ch.7), entry 0x02 (Output Overload))
UINT32
RO
0x6060:02, 1
1AE6:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6060 (AO Inputs Ch.7), entry 0x03 (Underrange))
UINT32
RO
0x6060:03, 1
1AE6:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6060 (AO Inputs Ch.7), entry 0x04 (Overrange))
UINT32
RO
0x6060:04, 1
1AE6:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1AE6:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6060 (AO Inputs Ch.9), entry 0x06 (Warning))
UINT32
RO
0x6060:06, 1
1AE6:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6060 (AO Inputs Ch.7), entry 0x07 (Error))
UINT32
RO
0x6060:07, 1
1AE6:08
SubIndex 008
UINT32
RO
0x0000:00, 9
*) EL4078 only
Index 1B07 AO TxPDO Map Status Ch.8*)
Index (hex)
Meaning
Data type
Flags
Default
1B07:0
PDO Mapping TxPDO 264
UINT8
RO
0x08 (8dec)
1B07:01
SubIndex 001
UINT32
RO
0x0000:00, 1
1B07:02
SubIndex 002
PDO Mapping entry no. 2 (object 0x6070 (AO Inputs Ch.8), entry 0x02 (Output Overload))
UINT32
RO
0x6070:02, 1
1B07:03
SubIndex 003
PDO Mapping entry no. 3 (object 0x6070 (AO Inputs Ch.8), entry 0x03 (Underrange))
UINT32
RO
0x6070:03, 1
1B07:04
SubIndex 004
PDO Mapping entry no. 4 (object 0x6070 (AO Inputs Ch.8), entry 0x04 (Overrange))
UINT32
RO
0x6070:04, 1
1B07:05
SubIndex 005
UINT32
RO
0x0000:00, 1
1B07:06
SubIndex 006
PDO Mapping entry no. 6 (object 0x6070 (AO Inputs Ch.8), entry 0x06 (Warning))
UINT32
RO
0x6070:06, 1
1B07:07
SubIndex 007
PDO Mapping entry no. 7 (object 0x6070 (AO Inputs Ch.8), entry 0x07 (Error))
UINT32
RO
0x6070:07, 1
1B07:08
SubIndex 008
UINT32
RO
0x0000:00, 9
*) EL4078 only
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x08 (8dec)
1C12:01
Subindex 001
Assigned RxPDO no. 1 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1622 (5666dec)
1C12:02
Subindex 002
Assigned RxPDO no. 2 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1646 (5702dec)
1C12:03
Subindex 003
Assigned RxPDO no. 3 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x166A (5738dec)
1C12:04
Subindex 004
Assigned RxPDO no. 4 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x168E (5774dec)
1C12:05
Subindex 005
Assigned RxPDO no. 5 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x16B2 (5810dec)
1C12:06
Subindex 006
Assigned RxPDO no. 6 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x16D6 (5846dec)
1C12:07
Subindex 007
Assigned RxPDO no. 7 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x16FA (5882dec)
1C12:08
Subindex 008
Assigned RxPDO no. 8 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x171E (5918dec)
1C12:09
Subindex 009
Assigned RxPDO no. 9 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0A
Subindex 010
Assigned RxPDO no. 10 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0B
Subindex 011
Assigned RxPDO no. 11 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0C
Subindex 012
Assigned RxPDO no. 12 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0D
Subindex 013
Assigned RxPDO no. 13 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0E
Subindex 014
Assigned RxPDO no. 14 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:0F
Subindex 015
Assigned RxPDO no. 15 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C12:10
Subindex 016
Assigned RxPDO no. 16 (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x08 (8dec)
1C13:01
Subindex 001
Assigned TxPDO no. 1 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A20 (6688dec)
1C13:02
Subindex 002
Assigned TxPDO no. 2 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A41 (6721dec)
1C13:03
Subindex 003
Assigned TxPDO no. 3 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A62 (6754dec)
1C13:04
Subindex 004
Assigned TxPDO no. 4 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A83 (6787dec)
1C13:05
Subindex 005
Assigned TxPDO no. 5 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1AA4 (6820dec)
1C13:06
Subindex 006
Assigned TxPDO no. 6 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1AC5 (6853dec)
1C13:07
Subindex 007
Assigned TxPDO no. 7 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1AE6 (6886dec)
1C13:08
Subindex 008
Assigned TxPDO no. 8 (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1B07 (6919dec)
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameter for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: free run
  • 1: Synchronous with SM 2 Event
  • 2: DC mode – synchronous with SYNC0 Event
  • 3: DC mode – synchronous with SYNC1 Event
UINT16
RW
0x0001 (1dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free run: cycle time of the local timer
  • Synchronous with SM 2 Event: cycle time of the master
  • DC mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x000F4240 (1000000dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: Free Run is supported
  • Bit 1 = 1: Synchronization with SM 2 event is supported
  • Bit 2–3 = 01: DC mode is supported
  • Bit 4–5 = 10: Output shift with SYNC1 event (DC mode only)
  • Bit 14 = 1: dynamic times (measurement through writing of 1C32:08)
UINT16
RO
0x0002 (2dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:09
Maximum delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C32:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC Mode only)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of intervals between SYNC0 and SYNC1 events that are too short (DC Mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC Mode only)
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameter for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: free run
  • 1: Synchronous with SM 3 Event (no outputs available)
  • 2: DC – synchronous with SYNC0 Event
  • 3: DC – synchronous with SYNC1 Event
  • 34: Synchronous with SM 2 Event (outputs available)
UINT16
RW
0x0022 (34dec)
1C33:02
Cycle time
  • as 1C32:02
UINT32
RW
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, DC Mode only)
UINT32
RO
0x00000000 (0dec)
1C33:04
  • Bit 0: Free Run is supported
  • Bit 1: Synchronization with SM 2 event is supported (outputs available)
  • Bit 1: Synchronization with SM 3 event is supported (no outputs available)
  • Bit 4–5 = 01: Input shift through local event (outputs available)
  • Bit 4–5 = 10: Input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 1C32:08 or 1C33:08)
UINT16
RO
0x0002 (2dec)
1C33:05
Minimum cycle time
as 1C32:05
UINT32
RO
1C33:06
Calc and copy time
Time between reading of the inputs and the inputs being made available for the master (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C33:09
Maximum delay time
Time between SYNC1 event and reading of the inputs (in ns, DC Mode only)
UINT32
RO
0x00000000 (0dec)
1C33:0B
as 1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
as 1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
as 1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 1C32:32
BOOLEAN
RO
0x00 (0dec)
Index F008 code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
Code word (currently reserved)
UINT32
RW
0x00000000 (0dec)
Index F009 Password protection
Index (hex)
Meaning
Data type
Flags
Default
F009:0
Password protection
Password protection user calibration
UINT32
RW
0x00000000 (0dec)
Index F081 Download revision
Index (hex)
Meaning
Data type
Flags
Default
F081:0
Download revision
Max. subindex
UINT8
RO
0x01 (1dec)
F081:01
Download revision
The subindex 0xF081:01 (Download revision) describes the revision level of the module.
UINT32
RW
0x00000000 (0dec)