AI Status PDO of the power supply outputs (ED3072)
The ED3072 EtherCAT device has two power supply outputs, each with individual overcurrent protection, for 20 mA sensors.
For the ED3072 EtherCAT device, a 16-bit status PDO can be added to the inputs for each power supply output. The status PDOs for the power supply outputs are disabled by default. The optional “AI Output Status Channel n” PDOs can be enabled on a per-channel basis. Proceed as follows:
1. Select Sync Manager 3 “Inputs” in the “Process Data” tab
2. Retrieve the corresponding indices 0x1A21 and 0x1A23 from the “PDO List” field
3. Enable these using the checkboxes in the “PDO Assingment (0x1C13)” field
the new process data are visible in System Manager as variables that can be linked
after activating the configuration and restarting TwinCAT or the EtherCAT master, the new process data becomes active
AI Status PDO of the power supply outputs (ED3072) 1:
Fig.35: ED3072 – selecting the “AI Output Status Ch n” PDO display for the power supply outputs
The status PDOs are used to indicate to the controller when the respective power supply output is overloaded. This means that the output voltage is < typically 15 V. In addition, a DiagMessage is sent (see Fig. “ED3072 – DiagMessage when the power supply output is overloaded”).
Bit
Size [bit]
Data type
Status.0–5
Status.6
Error
1
Set when overloaded
Status.7
Status.8
Output overload
1
Set when overloaded
Status.9–15
AI Status PDO of the power supply outputs (ED3072) 2:
Fig.36: ED3072 – DiagMessage when the power supply output is overloaded